K
Kelrich
morning all
i have a problem with the lights in a house firstly they wouldnt seperate as theres a borrowed neutral on upstairs circuit so had to put them into same mcb now when doing my zs test it keeps tripping the rcd any help please
metrel easitest mi3000 has a zs rcd function to avoid tripping but it still trips it was fine on rest of circuits just the lights
It sounds like there is a unbalance somewhere try testing mid circuit (if lights have been 3 plated) with switches turned off just to see if it still trips.
Is there a way you can get into the setting on your test kit and change the UL from 50v to 25v and carry out the test again I had a ethos 7920 which used to have to do this to when i was testing circuits in swimming pools protect by 10mA RCDs on that you pushed a button on start up. If you dont have this option test the RCD at 1/2 * if its ok turn everything off link out the rcd and just energize circuit you want to test. It wont trip then