i have just watched their periodic inspection DVD today, and the same situation regarding Zs was reiterated in this one also.

Dont get me wrong i have no problems testing live for Zs but their information seems to contradict the scenarios their local inspectors will put us in apparently.
 
can anyone answer the question below.
Calculate from the data below, the earth loop impedance of a radial circuit installed using 2.5mm conductors for line and CPC. show all calculations
Data
Ze 0.15 cable length 25m, conductor resistance 7041mΩ/m
 
Most people on this site could work it out Gtbadboy1, but you should be working it out yourself.
You've been given your conductor resistance per meter, multiply that by the length of the line conductor plus the length of the cpc, then add this to your Ze.
 
either i am thick , short-sighted or what. the res.of the cable is given as 7041 mohms/m i.e 7.041ohms/m. is it copper or string? this gives R1+R2= 3705ohms
 
Last edited:
o.37 then. add o.15, Zs=0.52 ( multiply for the correction factor allowing for stretching due to the fact that the cable was 3" too short to terminate, )
 
on my assessment, the nic man said that the nic would rather you do a ze and add it to an r1/r2 to get zs, its less live testing

On this occasion NICEIC are having to stick with their DVD productions. It's up to your interpretation on what you consider best practice.
MCB's and RCD's can give off impedances that will provide a higher measured Zs than the simple calculation will prove.

I would go into the NICEIC's reasoning, however I dont have my EAW redgs in front of me so don't want to start misquoting them.


Oh and its (R1&R2) btw.
 

Reply to Zs tests on radial circuits? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
830

Similar threads

Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K
Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
685

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top