Why is that?
0.8ze for a distribution circuit is quite high with other circuits coming off it, maybe not now but in the future when they go to expand.
just did a quick google search and 4c 70mm swa is £23m.
for 500m thats 12.5k surely it might have been a better design for another supply from the grid.
especially if they only needed a 30amp supply
for 500m thats 11k surely it might have been a better design for another supply from the grid
Or two cables in parallel maybe. Back in the day when I was subbing we once pulled in a cable cant remember the distance but I know the cable cost 12k and it come up about 50meters shy of where it was supposed to go lol. Btw the measuring/ordering of the cable had nothing to do with me lol.
but the OP said he was putting in an upfront rcd would that not cover the disconnection time for all final circuits aswell , saying that i don't think the design is the best but we don't know the resons for the design and there could well be a good reason fot it
true but i cant see why the original installer did this
To complete this issue I've been in touch with Schnieder as it was there MCCB in the panel, they have provided a Vigirex unit with a Toroid and a shunt trip. This is a essentially a earth current monitoring device rated from 0.3-1 amp and the shunt trip attaches to the MCCB to activate the tripping mechanism.
Hi the original installer, has made a huge mistake. I can only assume because he was separating the earth at the load end and creating a TT ( again not sure why as it is a TN-S system, lack of research i think.) he thought that he didnt require the Zs value at the end of the supply cable.
Reply to Zs to high on MCCB Protected circuit? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
What readings were you expecting for the cable prior to testing? What is the make of the protective device? Is there any previous paperwork [test...
I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...