Not certain if the Ze of 0.08 is the measured value, or reference to the given value of 0.8 for TN-S systems?
 
thanks for all your input guys, this site is a great help to someone who is not ashamed to admit that I have only recently got my City & Guilds (In response to Tonys question, "am I an electrician?", no I feel as though I've still got a lifetimes learning ahead of me still, but find this whole subject fascinating. Cheers
 
From looking at your post No. 14 re. the Zs at individual boards, I would imagine that it was measured.
 
Yes, you would never get 0.08 Ohms by enquiry.

The earthing conductor size is not an issue as regards Ze/Zs.

What is the type of the BS 3871 devices?
 
So you have 2 DB's with exceeded maximum Zs values.

Are these DB's much more remote or supplied by smaller CSA distribution circuits?

I'm really asking if this is down to poor design or cpc continuity faults on the distribution circuits in question...
 
It may be possible to reduce the Zs by the installation of supplementary bonding.
 
I want to know the reason for the high Zs before he starts stringing green/yellow to the nearest sink! ;)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Zs too high at distribution boards
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
43

Advert

Thread statistics

Created
knasher,
Last reply from
Dave_,
Replies
43
Views
14,239

Advert

TrueNAS JBOD Storage Server

Back
Top