Zs too high | on ElectriciansForums

Discuss Zs too high in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Joined
May 21, 2024
Messages
5
Reaction score
0
Location
uk
I have a Ze reading of 0.35 on a TNCS system and I've had the DNO out to check and they say its ok.

From my main board I have 2x 10mm sub mains feeding another board and my Zs on the cables is ~0.45 ohms. Max allowed according to BS7671 is 0.35 ohms. What can I do in this instance as the high Zs is caused by the high Ze which the DNO has okayed.

Thanks for the input.
 
I have a Ze reading of 0.35 on a TNCS system and I've had the DNO out to check and they say its ok.

From my main board I have 2x 10mm sub mains feeding another board and my Zs on the cables is ~0.45 ohms. Max allowed according to BS7671 is 0.35 ohms. What can I do in this instance as the high Zs is caused by the high Ze which the DNO has okayed.

Thanks for the input.
Where does BS 7671 stipulate any such limit? (And incidentally, you have already stated that the DNO have met this imagined "limit".)
 
Submains have a Zdb, not a Ze. You mention the submains are fed from the main CU, so as long as your ~0.45 ohm Zdb is suitably low that the protective device feeding the submain will trip within the time (assuming 5s for distribution circuits on this TNC-S) and the adiabatic says the 10mm will survive under that fault current for the time, then to my understanding all is well.
 

Reply to Zs too high in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
389
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
707
  • Question
Just re-read the OP's post and it is an existing 5C SWA so presumably a 3P supply. For 40A and 150m you are seeing 6.6V drop or 1.65% of 400V 3P...
Replies
8
Views
893

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top