Can anyone advise or explain the correct procedure to carry out the above tests on a megger 1720?
I recently purchased a megger 1720 and thought I would have a play with it at home before taking it on site. When carrying out z tests it give you a choice of 2 and 3 lead hi and low test all giving you different results I had a quick look in the distractions but thought you guys and girls may have a bit more experience and be able to explain in pracical terms.
 
I have an MFT 1731.

For Ze (for measuring Ze, PEFC and PSCC) you should use the two lead hi current mode. For Zs you should aim to use the two lead hi current test if the circuit is not RCD protected and the three lead low current test if it is.

The three lead low current test is not as accurate as the two lead hi current, but it shouldn't trip RCDs (which can adversely affect the test results which is why you'll find information in various threads here about bypassing RCDs and using the two lead hi current test).

Hope that helps.
 
now daddy boy .the pipes are calling you from glen to glen ,
new Megger ?
Funny i was actually named after that song any way.... I was using a metrel before but bought this one from someone at the wholesalers. Just trying to get my head round it as it seems a lot more complicated then my other one!
 
Funny i was actually named after that song any way.... I was using a metrel before but bought this one from someone at the wholesalers. Just trying to get my head round it as it seems a lot more complicated then my other one!
its the simplistic tester you can use . go on the webb
type in megger 1720 manual .
 
Yellow has been made a little more cool by the
"Minions"
yeah ,but made by this guy.
[ElectriciansForums.net] Zs /  Ze 1720 confusion
 
meggers bfore the 1700 series used to need 3 wire test for no trip. just bear in mind that, due to the much lower current used in any no-trip test, the results may not be accurate due usyally to some contact resistance which is overcome when performing a hi current test.
 

Reply to Zs / Ze 1720 confusion in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top