Hi, when Installing a fused down spur off a rfc, do you record the max zs for the 32a mcb or the bs1362 fuse? Had different opinions on this!
 
Ah ha, a very good question indeed. Presumably its a MWC you are completing.

I would record the protective device as the fuse value in the FCU and the Zs is taken at the end of the fused down spur.
 
Can I assume you mean a Fused Connection unit / Fused spur, for a boiler or an alarm etc?

Then your Zs will be measured at the supply side not the load side connections, and as post above states (the one before murdoch got in!) you record the highest measured Zs, which if you have spurred off a ring will be at your spur unless you have more than one spur.

The maximum allowed Zs will be that for the circuit protective device protecting the ring including your spur as per the table in the on site guide. The output side of the spur has no relevance as the fuse fitted is only there to protect the flex to whatever you are supplying, which is the same as if you were to plug an appliance into a socket.

Cheers...........Howard
 
Last edited by a moderator:
Can I assume you mean a Fused Connection unit / Fused spur, for a boiler or an alarm etc?

Then your Zs will be measured at the supply side not the load side connections, and as post above states you record the highest measured Zs, which if you have spurred off a ring will be at your spur unless you have more than one spur.

The maximum allowed Zs will be that for the circuit protective device protecting the ring including your spur as per the table in the on site guide. The output side of the spur has no relevance as the fuse fitted is only there to protect the flex to whatever you are supplying, which is the same as if you were to plug an appliance into a socket.

Cheers...........Howard

Yes fused connection unit, taking lights from it as cant disturb floor or ceiling, I will take r1+r2 at furthest light and ir test , but wondered whether to record zs at furthest light or at spur and like I said can't find a max zs for fuse bs1362 but I have been told both ways
 
sir kit is correct. record R1+R2 and Zs at furthest light, but the max. Zs is that for the 32A MCB at the origin of the circuit. 1.44 for a B type ( less temp. correction if you use the osg figures)
 

Reply to Zs in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
693
Thank you everyone for your comments Celia
Replies
6
Views
662

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top