Hi, when Installing a fused down spur off a rfc, do you record the max zs for the 32a mcb or the bs1362 fuse? Had different opinions on this!
 
Yes fused connection unit, taking lights from it as cant disturb floor or ceiling, I will take r1+r2 at furthest light and ir test , but wondered whether to record zs at furthest light or at spur and like I said can't find a max zs for fuse bs1362 but I have been told both ways

Keith,

Nothing wrong with wanting to go the extra mile with your testing. as long as the Zs is in spec for your spur, then you wont have any probs with going out of spec for Zs on fuse for your lights, unless the circuit is excessively long.
Whatever fuse is fitted wont blow before the MCB trips at the CU anyway, or it is very unlikely to.

Cheers...........Howard
 
Last edited by a moderator:
Whatever fuse is fitted wont blow before the MCB at the CU anyway


​all depends on the current. if it's overload and under 40A , it will be the 5A fuse that goes. last week i had a blown lamp blew 2 3A 1362's and took out the 16A MCB in the CU all together.
 
won't disagree, murdoch, but the max. value you enter on your cert is for the whole circuit, from origin at CU, not from the FCU fuse.
 
Thanks everyone! So just to clarify you disregard all test results for the output of the fused spur zs wise and record the zs at the supply side of it?

Could be feeding a further socket outlet or light rather than an appliance. In such a case, no.
 
Last edited:
Sorry assumed he was asking the max permissable value of zs to record on the test sheet and not where to test which is obv furthest point/highest value, but still if the mcb max permissable value was recorded it would be a lower value which would presumably be met anyway
 
Sorry assumed he was asking the max permissable value of zs to record on the test sheet and not where to test which is obv furthest point/highest value, but still if the mcb max permissable value was recorded it would be a lower value which would presumably be met anyway

So furthest point would be the light in this case, max zs would be 1.93 for the fuse and 1.15 for the mcb, iv always had mixed replies on this just thought I would start a debate! I have always tested at the end of the circuit even after a spur if I'm honest
 

Reply to Zs in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
693
Thank you everyone for your comments Celia
Replies
6
Views
662

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top