Discuss 3-phase cable calculation in the UK Electrical Forum area at ElectriciansForums.net
Hi,
A while ago I posted about my neighbours 3-phase generator etc....
So he's being running through diesel like there's no tomorrow and been talking to a local barn who have said he can take the power from his property to supply their kiln.
He's been measuring the his average usage over the last month or so, an on average his kiln uses 12kw, so we will run a cable for a 15mw supply to side on caution.
So he wants to bury a 3-phase supply to the kiln from the barn. The barn is roughly 1000m away. I wanted to check to see if I'm calculating the cable size correctly.
15kw/400 x 1.73 = 64.9amps
So Woud that be 21.6amps Per phase?
I'm struggling to work out volt drop to determine the CSA of the cable?
Hi,
No
But he can't be using 12kw per phase, so wouldn't that be the total split between phases?
His current kiln is supplied via a 20kw diesel generator. When I was there before Christmas I measured the current on each phase at that point of time and it was only like 7-8kw between all 3.
I was thinking round 16mm to handle the voltdrop. So what I wanted to check, the current requirements its asking for, I'm guessing that's 21.6amps rather than 64.9amps. As there's a massive difference between 25mm and 95mm!
16mm is nowhere near big enough to handle the volt drop of a 1km cable route. Then the next problem will be how you overcome the earth loop impedance issue.
I suggest you do some calculations to size the cable correctly and then look at how you are going to protect said cable against an earth fault.
On a positive note, I do think you installing a 15MW supply (as per your original post) is a bit overkill!
You say you have clamped the load per phase, did you assess how the kiln and its controls work?, did you check all elements were in working condition and calling heat when you clamped?
Simply clamping on a temperature controlled kiln may not give you the max demand unless you are familiar how it exactly works.
Are the elements 400v or 230v, do they have 2 x 230 in series across 2 phase, an element down could effectively would take out 2 elements.
This is all before you even get to the cable size, as is the nature of such equipment it is crucial to find out if it is across the phases or per phase, assumption can be a costly kick in the nether regions.
The kiln has small electrical draw. There 400v fans which circulate the heat, the source of file is chipping a from a small hydronic shaft. When I measured it, everything was set to maximum demand, so the desired temp was set above max output so would have thought that would have been the highest demand even with the shaft in operation
If you are unsure then open the controls find the element connections and visually inspect the elements for links which my not come back to the controls, work out how they are connected and test them thus you have the values you need to work out the current required.
Don't get me wrong here, I'm not trying to trip you up, I never like the term 'I thought' 'I assume' 'I guess' when members are giving what is vital info in order for us to respond, like I said, how do you know you don't have a bank of elements down, the balance of the current demand would suggest not but there exists ways to connect the elements that would still leave a balanced load if an element failed.
You need to know how many elements are in the kiln, the wattage of them and the voltage, plus how they are connected, the uncertainty you have about the info supplied means you will have to work it out yourself.
there is no elements in the kiln, the kiln is formed from 2 containers. One houses the fuse board, a large furnace with a storage area with wood chipping. The furnace burns 24/7, and there's a small shaft which basically pushed chippings every so often into the furnace to keep it burning. Then the heat from the furnace travels through a duct powered by 2 fans into the secondary container unit, which is used to store logs which are dried out.
Ok more info now which creates more questions, what are the ratings of the 2 motors?
I assume you mean an Auger when you say shaft (like an helter-skelter inside a tube) when it turn it pulls the fuel through, this will also have motors on it but tend to be small in my experience.
Motors been inductive loads with inrush to start up will need you to make sure VD is correct.
Hi,is this a pellet/chip processor?
If so,it's power needs would be different to an actual "kiln"
Hi,
Are you sure the barn is 1000mtrs away, not 100mtrs?
If the barn is 1000mtrs then for the 15kw supply you would require a minimum 70mm2 cable. But this gives you the bare minimum supply voltage so more information is required to do an accurate calc. Once other things are factored in i.e routing of cable, type of load, power factor of load...you are probably looking at more like 95mm2 as Lee stated. @ around £30 x 1000mtrs = £30k just for the cable! This is about the same cost as 6500 gallons of red diesel.
Reply to 3-phase cable calculation in the UK Electrical Forum area at ElectriciansForums.net
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...