Hi,

A while ago I posted about my neighbours 3-phase generator etc....

So he's being running through diesel like there's no tomorrow and been talking to a local barn who have said he can take the power from his property to supply their kiln.

He's been measuring the his average usage over the last month or so, an on average his kiln uses 12kw, so we will run a cable for a 15mw supply to side on caution.

So he wants to bury a 3-phase supply to the kiln from the barn. The barn is roughly 1000m away. I wanted to check to see if I'm calculating the cable size correctly.

15kw/400 x 1.73 = 64.9amps

So Woud that be 21.6amps Per phase?
I'm struggling to work out volt drop to determine the CSA of the cable?

Thanks
 
Hi,

A while ago I posted about my neighbours 3-phase generator etc....

So he's being running through diesel like there's no tomorrow and been talking to a local barn who have said he can take the power from his property to supply their kiln.

He's been measuring the his average usage over the last month or so, an on average his kiln uses 12kw, so we will run a cable for a 15mw supply to side on caution.

So he wants to bury a 3-phase supply to the kiln from the barn. The barn is roughly 1000m away. I wanted to check to see if I'm calculating the cable size correctly.

15kw/400 x 1.73 = 64.9amps

So Woud that be 21.6amps Per phase?
I'm struggling to work out volt drop to determine the CSA of the cable?

Thanks
No
 
But he can't be using 12kw per phase, so wouldn't that be the total split between phases?

His current kiln is supplied via a 20kw diesel generator. When I was there before Christmas I measured the current on each phase at that point of time and it was only like 7-8kw between all 3.
 
I was thinking round 16mm to handle the voltdrop. So what I wanted to check, the current requirements its asking for, I'm guessing that's 21.6amps rather than 64.9amps. As there's a massive difference between 25mm and 95mm!
 
I was thinking round 16mm to handle the voltdrop. So what I wanted to check, the current requirements its asking for, I'm guessing that's 21.6amps rather than 64.9amps. As there's a massive difference between 25mm and 95mm!

16mm is nowhere near big enough to handle the volt drop of a 1km cable route. Then the next problem will be how you overcome the earth loop impedance issue.
I suggest you do some calculations to size the cable correctly and then look at how you are going to protect said cable against an earth fault.

On a positive note, I do think you installing a 15MW supply (as per your original post) is a bit overkill!
 

Reply to 3-phase cable calculation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
336
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
1K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
25
Views
1K
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock