Low insulation resistance reading

Discuss Low insulation resistance reading in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
21
Hello everyone,

Hope you're all well.

I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did recently. I joined all 3 phase together to neutral and tested from the busbar to earth.

I'm getting a reading of 1.33MOhms, and here in Ireland, we require a minimum of 2Mohms. I had disconnected the surge protection device previous to that. It is all RCBOs for lighting and sockets. A couple of 3 phase mcbs feeding coffee machine and oven but no appliances plugged in.

When I turned off all the mcbs and rcbos and tested busbar to earth again, I'm still getting the same reading of 1.33Mohms. Any idea what could be causing this? Is it something in circuit? Because I do have many lamps, leds etc in circuit. Is it best to disconnect all of these, which would be a monumental pain in the hole, or should the 3 phases together to neutral not negate that?

Thanks all.
 
4 pole main switches are fairly common here, but the point was more about the fact we're free to use them, whereas I believe they can not be used in IE.

I wouldn't say free to use, you would only switch the neutral when absolutely necessary.
Switching the neutral introduces a greater risk of losing the neutral to the load whilst the phases are still connected thus damaging the load.
 
There is always a non-zero chance of a fault happening.

And why would you need to switch the neutral on a TN supply?

That's part of the reason why I'm raising this point. I'm under the impression that it isn't permitted in IE, where the vast majority of supplies are TNC-S, but I see plenty of 4 pole isolation on TN supplies in the UK.

I have questions to ask which expand on this and don't wish to hi-jack the OP's thread more than has already happened. It's not a subject I've seen under much discussion on the forum, so have started a thread and would welcome any input.

 
That's part of the reason why I'm raising this point. I'm under the impression that it isn't permitted in IE, where the vast majority of supplies are TNC-S, but I see plenty of 4 pole isolation on TN supplies in the UK.

I have noticed a trend towards installing 4 pole main switches where until a few years ago 3 pole would always have been preferred.
 
On a TT you need to isolate all conductors including the neutral, hence the switch where the neutral contact is set back so it closes early and breaks late, relative to the 3 phases.
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for us sparks to discuss for sure.
 

Reply to Low insulation resistance reading in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock