Hi, I am a trainee electrician and have some questions concerning a 3-phase installation. I have been asked to calculate the maximum load of a supply at a factory and have the following information. I realise the best option is to use a clamp meter and measure the voltage and current load across each phase.. this is something i intend to do on our next visit to the site.
My question is this.. There is a 3-phase 70Kva service line installed on 35mm swa.
there are 4 main lathe machines and several single phase loads.
the machines power and current ratings are:
1) Hardridge Gx150 power 21Kw, load current 38 A
2) Hardridge Gx600 power 21Kw, load current 42 A
3) Bridgeport power 19Kw, load current 40 A
4) Bridgeport power 10Kw, load current 30 A
5) Proteus power 12Kw load current 63A
I am using the following formula for KVA: = (V*I*√3)/1000 where √3 = 1.732
the kva figures I obtained are 26.25, 26.25, 23.75, 12.5 and 15.2 respectively.
Making a total of 103.87Kva....???
This is way over the 70Kva plus if I add all the figures I have calculated fo rthe single phase boards, the total Kva goes up to 173.45 Kva
This does not make sense to me can someone please explain or show me where i have gone wrong..
many thanks..
many thanks..