Search the forum,
Discuss 305 Design Assignment guidance needed in the Electrician Courses : Electrical Quals area at ElectriciansForums.net
Hi I'm currently doing C&G 2365 Level 3
I'm working through the 305 design assignment (Swimming pool, hotel etc.)
Other then this assignment I have 1 exam for inspection and testing and a few practical days before completing.
I have done a fair few searches on google about this project a lot of the time bringing me to this forum.
I just wanted to check I'm doing these questions correctly. I feel confident with most except a few
Q2 d. Show how each circuit in the new hotel extension is to be arranged.
Is this asking to draw the circuits? I have done it this way. So from a submain in the hallway cupboard, distribution circuits to db's in each room (in purple). Then from the submains inside rooms, 1 circuit from the db to each socket outlet and fcu (in green). 1 circuit from db to air handling unit (fused spur) in red.
Then Q3 select with the aid of manufacturers data, suitable protective devises for this contract.
I was going to use 61009-1s for all final circuits, 60898s or 88s for distribution circuits supposing they dont require rcd protection, I assume surface run etc. Also 60898 for fire alarm circuit.
And finally filling out the table Q4
Ib is P/V
In should be equal to or greater then Ib
It is tabulated current worked out from In/Ca x Cg etc.
Iz is the curent carrying capacity of the chosen cable + method of installation?
I can upload pictures if need be.
Thankyou very much!
Sam
Hi Sam,
Also in the process of doing this.
You have to show calculations for all the circuits within the table. Took me a very long time, still actually completing the calculations.
The drawings sounds like you’ve done them right, just remember with the pool/cafe to keep circuits under 30m. I had to add either more boards or split the circuits to stay in this. The specifications does give you all the details you need. Don’t forget the drops to the switches.
61009-1 for every circuit is fine as well. You have to use manufacturers data to provide reasoning why you’re using it and if it meets the Pfc. I’m just about to do this so will happily update you once it’s marked.
For the calculations, I’ll check what I’ve done and update you as I’ve had it marked and okayed for the circuits I’ve done so far.
About to take in question 6 diversity so need advice on that as well.
All the best and will update you on calcs asap
Andew
Hi Sam,
Andew
Thanks for the reply mate! Been a bit busy lately so haven't got much more done. I missed the 30m limit at first but was only lighting that exceeded so easily changed. I've done most of the calculations now just need to do the basement area. I'm guessing I'll have to do calcs for my distribution circuit down there to determine the Zs and Pfc of the final circuits.
Did you have to apply the factor for conductor resistance at maximum operating temperature? Wo calculate r1+r2. I applied the factor for ambient temperature and then again for maximum operating temperature but think I should have left out the ambient temp factor...
I can send you my calcs and see how they compare?
Hi both, I am currently doing the same project! did a post last week but no reply sadly. i would be grey grateful if you could help provide some guidance as i am struggling on some questions. i am also a bit worried that the drawings need to be done to scale which i havnt done. any help at all will be amazing. this is for the hotel extension project 😃
Ib is P/V
Thankyou very much!
Sam
Ib is P/V
Thankyou very much!
Sam
Hi Sam,
I am also doing the same project on design assignment unit 305 2365 level 3. if you could help me with this projects? i am bit confused regarding circuit summary and names and what shall i add to the list. thank you for you help in advance and really appreiated.
Reply to 305 Design Assignment guidance needed in the Electrician Courses : Electrical Quals area at ElectriciansForums.net
Hi, I'm doing my Level 3 Electrical Install course, and I'm doing distance learning so most of the work is being done by myself with no guidance...
Hi, I am finishing up my design drawing for submission. I am working out all my circuit calculations and am a bit confused about what size I...
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and...
4K
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
8K
Electrical Courses