Search the forum,
Discuss Advice on Shed Wiring in the UK Electrical Forum area at ElectriciansForums.net
Hi,
I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would appreciate any more experienced view to check my logic.
My house was professionally rewired in 2022, but I would like to connect a small 8x6ft shed to a secondary CU that's close by. Connecting to the main CU would require too much upheaval.
The shed is small, but I'm planning to install a few sockets for charging power tools and occasional use of garden tools - plus an internal and external light. No big loads.
Obviously, it's a very simple issue, but I'd appreciate a more experienced view on any issue with my connecting to the secondary CU. The 12m SWA run is clipped externally but fiddly with tight access, so keeping that deliberately light also. Just keen to avoid anything daft before my friend sees it!
Many thanks in advance.
Am I seeing 3 RCDs in series there 😁
Quite right - seems this was a diagrammatic error upon checking, thank you. On checking the secondary CU does not contain an RCD. I'm now thinking this is overengineered for my purposes and that I'll just put in some SWA, and my friend can hook up a simple radial circuit when he gets time. Much thanks.
Have you done the calculations on the 2.5mm SWA?
what else is on the secondary DB?
How far is the shed from the Secondary DB?
2.5mm2? nope not big enough, in fact allow for the future, get a decent size cable in there, again though what is on the Secondary DB?
Table 4E4 states greater than 32A for reference D, but that's only part of the story! just a starting point.
Its no wonder some people assume 2.5 will be fine on a 32A mcb.
PVC/SWA cable is quite rare now locally but can get it to order so now we just use xlpe/swa cable as standard.
But my point is a DIYer even a confident DIYer might not know the difference and assume any 2.5 cable is capable of greater than 32A when buried without considering other factors!
This is why I am a staunch supporter of the 'no advice to DIYers'. Unless someone is prepared to spend many hours on line with @thedawnbefore , going through the job at each stage, making sure it is done correctly, then the job is not going to be done properly or to the regulations (as it wont be notified or certified). This chap or lady may well be a thoroughly decent fellow with very good DIY skills, but he or she clearly doesn't understand electrics enough to be doing this.
There are so, so many factors involved here, from the depth of the buried cable (including cable warning tape) to Zs testing etc etc etc etc.
I think the only advice is to leave it fully to the electrician.
However, this is just my opinion and I am very open to fact I may be wrong. Perhaps it's best to give some basic info to DIYers. Perhaps this will decrease the chance of a dangerous situation. Personally, I think it is more likely to cause longer term problems. The DIYer gets more confidence, does more jobs, starts helping neighbours with electrics etc.
What a brilliant group, thank you for the interest in my issue. I’ve learnt a lot already from the feedback.
A 20A radial then from the second CU then. The SWA is clipped above ground so no issue there. It’s a short but awkward run hence my inclination to go light.
Reading between the lines, I should get my electrician friend to pop over first.
Thanks all 🙏
What do you mean by go light?
Are you suggesting you would install and undersized cable in order to make the job easier?
That was my inclination yes - I had understood from several calculators and manufacturer specs that 2.5mm 3-core clipped to external wall would be adequate for my couple of sockets to my shed? It would also be fused down appropriately.
While my main board is new and the secondary CU is on a 40A RCBO, would you put in another rcd at the shed end for good measure or is this pointless? My secondary CU which the shed is all mcbs and given this runs my heating, would be more than inconvenient if the shed sockets were to blow.
I will endeavour to consult my electrician friend in the design as you suggest. He struggles with English a bit though.
He struggles with English? My advice is pick a different one then!
It would likely be fine for a couple of sockets yes, it is definitely not fine for a 32A circuit though.
No I wouldn't install another RCD as that would not comply with the wiring regulations
Yes that will be inconvenient but with an RCBO at the supply end you are stuck with the risk of that happening, even if you put another RCD in the 40A RCBO will almost certainly trip first in a fault.
You may need to get someone else to help with the design of the job then, understanding the wiring regulations can be difficult even for some people who don't struggle with English.
So helpful and sincerely appreciated. Thank you.
Rest assured, I will get this checked and notified as part of a more complex battery install i'm having done professionally next month. I am a stickler for paperwork, and this is as much about my curiosity and wanting to learn and impress my electrician friend. Where I have done similar DIY in the past, qualified electricians have told me my work is perfect and have been happy to do the final CU termination and notify - but in hindsight, this was probably more luck than judgment as admittedly I had not involved them in the design. I respect the 2.5mm is controversial and not how others may do it. I've got to get the SWA round some very tight spaces though. I just want to avoid anybody finding an obvious 'bodge' or non-compliance.
I think this is the last question —would this new design be more appropriate? Should I put a corresponding MCB at the shed end in a waterproof DIN enclosure? A full CU seems overkill now, but from other installs I've observed, there should at least be a switch over there? I've updated my design below.
Thank you again and excuse my ignorance.
Heating ?? - Not an Off Peak supply is it by any chance as you could be back to square one!!
Good call out thanks. This CU is actually for an Air Source Heat Pump.
The contractor (not the guys who rewired the rest of the house) put in a great big 10 way CU for 3 ASHP MCBs. It's only on a 45A RCBO but the ASHP/Immersion never draws more than 15A. Obviously, it's less than ideal if it shuts my heating down, but I guess I can isolate the non-critical shed in the event there's a fault with it. It's only running a garden vacuum/pressure hose and some cordless chargers.
It is not controversial, nor is it a situation of being 'not how others would do it'. If you had followed your original design of a 32A MCB protecting the 2.5mm cable it would have been non-compliant and potentially dangerous.
However following your new design of a 20A MCB protecting the 2.5mm it is likely to be compliant and safe subject to confirmation.
Is there any particular reason it needs to be SWA?
Sould I put a corresponding MCB at the shed end in a waterproof DIN enclosure?
No, There is no point having a 20A MCB in series with another 20A MCB.
Why waterproof? If water is getting in to the shed then you should fix that before installing the electrics.
You'll probably want a light switch for the light but other than that no.
You will need to fuse down for the light but this could be done via a fused connection unit.
Thank you for another very helpful response. Just to assure you we are saying the same thing, I was referring to the 2.5 on 20A radial which I now understand to be technically compliant but still seems to be drawing criticism from some folks here. I respect it leaves little flexibility for future. I’m starting to think just put in 4mm
Actually no, come to think of it. It’s clipped to a wall/fence away from any mechanical interference. Squirrels perhaps.
Would you recommend an alternative e.g NYY-J? I’m not sure hard conduit will work and the flexible stuff would be unsightly for the neighbours
Reply to Advice on Shed Wiring in the UK Electrical Forum area at ElectriciansForums.net
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Hi, I'm a DIY'er looking to build a 6x8 shed in my backyard in Colorado. I'm installing a gravel pad first, with 4 concrete Sonotube...
Hi Everyone, hoping someone will be able to help me decipher the wiring for this hoist controller. the handset it came with has stopped working...
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...