Discuss Fault on Ring final circuit in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
89
Please advise what I should test / check next.

My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not contactable. I need to fix this asap. Ring final circuit tripping. I am not clueless and I have some test gear. Can fully isolate the supply with an isolation switch adjacent to the meter.

Circuit has worked fine until 2 days ago when temp wagos replacing an old socket were removed in a room being refurbed. This was purely to extend the wire by about a foot to get past new insulation. Not sure but I think the wire may have been pulled slightly during fixing new stud. The wire has since been stripped back about 20cm into the plastic conduit buried in the wall and no insulation damage can be seen. The ring has been made continuous at this point with Wagos (red to red, black to black and CPC to CPC) and carefully checked. Also tried it with a new socket. This is the only alteration to the circuit that has occurred.
Everything has been unplugged on the whole ring as far as I can tell.

This ring circuit serves about 25 double Hager sockets in 3 rooms of ground floor of house including the living rooms. Mainly used for plug in LCD lights and one LCD TV, so load is low. However, I don’t exactly know where the circuit goes as for example it also has at least one run to the attic (powers the internet router) and I expect it has at least 2 spurs. I have switched off the known fused spurs.

Circuit connects to 32A MCB on RH side of dual RCD Hager 16 way board installed and certified 2018 and checked 2022. However, wires to CU on this particular circuit are red/black and probably date back to circa 1998 when house was converted.

RCD trips if the ring circuit is connected to the MCB, or to another MCB, or to an MCB and different RCD on the other side of the board. MCB in off position. Still trips as soon as circuit energised. Cable is T&E 2.5mm with what looks like 1.5mm CPC but might be 1mm (see test results). CU wiring is not beautiful.

If live and neutral from this ring final are disconnected from the CU, (ie disconnect from neutral bar and MCB) nothing trips. We have other circuits in the house with RCBO CU’s and these are unaffected. These power the main load circuits luckily (eg kitchen and heating).

Using Megger MFT1711 (not in calibration), but leads checked and zeroed, full battery in tester, I have measured end to end resistance as follows:

r1 Live to live 0.96 ohms
rn Neutral to neutral 0.75 ohms
r2 CPC to CPC 1.9 ohms

I don’t know what these tested at when the CU was installed. These readings suggest to me that there is not a break in the circuit but I expected live and neutral readings to be closer. (I am not a pro obviously, but I have an engineering background in aeronautical electronics). rn being lower than r1 suggests a fault on the live circuit somewhere?

If CPC is 1mm then r2 is a ratio of 2.5 and a value of 1.875 (against rn) is close to the 1.9 ohms I measured for r2. If I do it against r1 then I get an expected very high r2 value of 2.4 ohms, which again suggests I have a problem with my r1 reading and fault on the live circuit?

Please advise what I should check next. Any advice and hints gratefully received. Thanks.
 
Last edited:
Please advise what I should test / check next.

My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not contactable. I need to fix this asap. Ring final circuit tripping. I am not clueless and I have some test gear. Can fully isolate the supply with an isolation switch adjacent to the meter.

Circuit has worked fine until 2 days ago when temp wagos replacing an old socket were removed in a room being refurbed. This was purely to extend the wire by about a foot to get past new insulation. Not sure but I think the wire may have been pulled slightly during fixing new stud. The wire has since been stripped back about 20cm into the plastic conduit buried in the wall and no insulation damage can be seen. The ring has been made continuous at this point with Wagos (red to red, black to black and CPC to CPC) and carefully checked. Also tried it with a new socket. This is the only alteration to the circuit that has occurred.
Everything has been unplugged on the whole ring as far as I can tell.

This ring circuit serves about 25 double Hager sockets in 3 rooms of ground floor of house including the living rooms. Mainly used for plug in LCD lights and one LCD TV, so load is low. However, I don’t exactly know where the circuit goes as for example it also has at least one run to the attic (powers the internet router) and I expect it has at least 2 spurs. I have switched off the known fused spurs.

Circuit connects to 32A MCB on RH side of dual RCD Hager 16 way board installed and certified 2018 and checked 2022. However, wires to CU on this particular circuit are red/black and probably date back to circa 1998 when house was converted.

RCD trips if the ring circuit is connected to the MCB, or to another MCB, or to an MCB and different RCD on the other side of the board. MCB in off position. Still trips as soon as circuit energised. Cable is T&E 2.5mm with what looks like 1.5mm CPC. CU wiring is not beautiful.

If live and neutral from this ring final are disconnected from the CU, (ie disconnect from neutral bar and MCB) nothing trips. We have other circuits in the house with RCBO CU’s and these are unaffected. These power the main load circuits luckily (eg kitchen and heating).

Using Megger MFT1711 (not in calibration) I have measured end to end resistance as follows:

Live to live 0.96 ohms
Neutral to neutral 0.75 ohms
CPC to CPC 1.8 ohms

I don’t know what these tested at when the CU was installed. These readings suggest to me that there is not a break in the circuit but I expected live and neutral readings to be closer. (I am not a pro obviously, but I have an engineering background in aeronautical electronics).

Please advise what I should check next. Any advice and hints gratefully received. Thanks.
The socket outlets may not be double pole, so wouldn't disconnect the neutral, so if you have a N to E fault it could continue to trip even though the outlets are turned off.

The first thing would be to disconnect every appliance and try again.

Disconnect the ring from the CU and Insulation test the wiring.

Split the ring at a near mid-point at one of the sockets and insulation test again work your way around the failing side.
 
Last edited:
Thank you. Not sure I understand. There is nothing plugged into any socket. Live, neutral and CPC are all disconnected currently from the CU on both sides of the ring. r1 is 0.96 ohms vs rn at 0.75ohms, which is more than suggested 0.5 ohm tolerance (as I understand it). As r1 is higher than rn, and as r2 gives an expected reading agaisnt rn, doesn't this suggest a defect on r1? Maybe a bad connection somewhere?

I expect I am bing dim here, but the only thing that has been touched since the circuit was working, was the one socket part of the ring (on wagos) being further extended from the wall. I have checked those wires, stripped them back a bit to give clean connection with wagos, and there is no visible fault.
 
r1 is 0.96 ohms vs rn at 0.75ohms, which is more than suggested 0.5 ohm tolerance (as I understand it).

In the text book and the classroom that is indeed an issue, in the real world however it barely worth raising an eyebrow.
Maybe a bad connection somewhere?

Probably a connection with a fractionally higher resistance, which you could spend a bit of time chasing down and improving, but it won't be causing the tripping problem.

The first steps to finding this kind of fault are pretty simple.
1 unplug everything/isolate all permanently connected loads.
2 IR test the circuit to establish a baseline reading of the fault.
3 remove a socket approximately halfway around the ring and desperate all conductors, IR test each leg at the CU and establish which half of the ring has the fault on it.
4 identify all sockets on the faulty half of the ring and further split that into 2 halves again, test each of these sections.
5 continue narrowing it down until you have either found a socket with a fault or a single section of cable with a fault.

Once you've done this you can then work out how to repair it.
 
You need to do an insulation resistance test (Do you have access to an insulation test meter) L-E, N-E (Mohms) rather than a continuity test.
As it is tripping without an appliance plugged in it would indicate most likely imo a N-E fault.

Splitting RFC as previously described by others would narrow it down.
 
Thanks all. The real world vs "textbook" is something I have no experience of in this field. The meter I have is a Megger MFT1711. I also have some Kew sockets that I can fit to sockets and plug the Megger into. To a degree I am having to gain experience in how to use this meter as I go along, being super careful, but I am sure it will do resistance tests.

My initial thought was a N-E fault so I was surprised when the r1 was higher than rn. The wiring in this house is a real jumble. All the new parts are perfect, but the old part of the house has been thoroughly DIY'd by the previous owner and his son.

I will get back on it first thing in the morning.
 
I would try a continuity test between the cpcs and neutrals you never know.
Agreed as that is what an IR test is doing, testing for any continuity between L-E, N-E.

Just trying to say End to End continuity tests don't help too much in this scenario.
 

Reply to Fault on Ring final circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
635
For some Strange reason we have three Circuits running in the Kitchen i think for two OLD Cookers and a Ring Circuit for the house. Well the...
Replies
18
Views
2K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
914
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
855

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock