I will do an IR test. That is helpful.

My amateur logic suggested that CPC was unlikely to be at fault as the resistance r2 was as expected vs rn.

It now transpires that although the CU has upstairs sockets on a different RCD to downstairs sockets according to the labels, the reality is that some upstairs sockets at one end of the house are out of action as well. CU clearly not labelled correctly. I think that the socket which started all this off, goes directly up to that area and it seems very likely to me that I will have to excavate that wire from the wall and conduit
 
Cables don’t generally break down for no reason… so the most likely issue is with a connection in the back of a socket, OR recent works have damaged a cable… any new things been screwed to the wall above a socket?

In the OP, it suggests that the circuit has been moved between mcbs and onto the other side rcd…
You may have left a neutral on the wrong N bar,
Each rcd supplies a bank of mcbs AND the corresponding neutral bar

You do say it’s a bit of a mess and you may have missed it.
 
Thanks liitlespark. Yes, I did move the entire ring across the CU to a different RCD to help eliminate RCD and MCB issues. I moved all six ends. It just tripped that RCD so very unlikely to be an RCD or MCB issue I felt. I had a spare 32A MCB on that side that I knew worked. All six ends are now disconnected from the CU so that I can have everything else powered up. I am very clear about which wires are on each side of the defective ring inside the CU. I am not a domestic electrician so I spend a lot of time double checking everything, including proving dead every time I do anything (I am working on my own).

Yes, studwork was put up in the room where the fault first emerged. I have added 150mm to 200mm internal insulation and panelling to the whole core of the house. The stud was actually fixed to an adjacent wall but tomorrow I will remove the panelling in the area and check that there has been no screw or nail gun penetration into the conduit. It's unlikely (I did all the studwork) and it is 200mm away from where the conduit is buried in the wall. However, I will check it in daylight. Thank you.
 
You had me worried there so I just went and removed the panel in that section of wall (which luckily was not glued to the stud - 2nd sight saved me). However, there are no nail or screw penetrations into the wall where the conduit is buried. But I can't help thinking the problem lies somewhere in that section of cable.
 
You had me worried there so I just went and removed the panel in that section of wall (which luckily was not glued to the stud - 2nd sight saved me). However, there are no nail or screw penetrations into the wall where the conduit is buried. But I can't help thinking the problem lies somewhere in that section of cable.
Only testing will tell for certain.

Some like to think and some like to do, the ones that do both are the ones who fix it.
 
:cool: I will definitely fix it. But please remember I am an amateur at DIY electrics and to a degree have to learn (courtesy of YT vids from GSH etc) as I go along. Hence it takes me ages to do what you guys would regard as obvious.

Naturally I want it all to be safe. Obviously I will get my electrician to check it when he gets back in February.
 
OK. Here is what is happening to me. I have disconnected all six ends from the CU as I don't want to test the whole board, just this one circuit. Neon bulbed spur is switched off (this feeds an outside socket). Nothing is plugged into any socket as far as I can tell. (Do I need to worry about switch positions on the sockets?)

MFT1711 has green and red leads plugged into same colour sockets, leads checked for OK and zeroed. Left dial set to 500v in the red zone. Right dial is on 30 in the yellow (but doesn't matter?) "Air test" shows 999 as expected. Tested together and I get a 0 (dead short) as expected so test leads OK and meter working.

Dividing the ring circuit into Left and Right I get:

Left side
L-N 0.00 M ohms
L-CPC 0.15
N-CPC 0.15
L+N-CPC 0.14

Right side
L-N 0.00
L-CPC 0.17
N-CPC 0.15
L+N -CPC 0.15

This suggests to me that I have a dead short on the live side somewhere? Is that correct? Even though L-L continuity seems to be OK as testing at o.81 ohms today.
 

Reply to Fault on Ring final circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
630
For some Strange reason we have three Circuits running in the Kitchen i think for two OLD Cookers and a Ring Circuit for the house. Well the...
Replies
18
Views
2K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
914
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
850

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock