Discuss Permanent Diesel Generators Installed Inside a Building in the Electricians' Talk area at ElectriciansForums.net
I have worked on a couple of jobs where back-up generators have been a requirement from the fire strategy document to power fire fighting lifts, smoke extract systems and sprinkler pumps. What particular requirements are you trying to find out?
Do somone know requirements for Permanent Diesel Generators Installed Inside a Building ?
Is this a Standby Set, or a Base Load set up? Things to consider:
Fuel Storage, tank bund needs to be sized so that it can contain all of the fuel in the storage tank, should there be a leak.
Signage, ensure all signage is up to standard.
H&S ensure you have the require First aid equipment.
Fire extinguishers, escape routes clearly marked.
Permit to work requirements, Adequate locks on doors etc, Only Authorised staff are allowed to enter unescorted.
Sighting of exhaust system, ease of access to building.
Reply to Permanent Diesel Generators Installed Inside a Building in the Electricians' Talk area at ElectriciansForums.net
Hi all. Slightly out of the ordinary, but I'm looking to replacing between 60 to 100 standard size E27 bulbs with LED equivalent. The catch is...
No waffling, going to get straight to the point. Main water on the exterior of the building in plastic. Changes to copper inside the building...
I'm an electrical engineer in training so please bear with me. Basically, a bank has ordered a second 500kw diesel generator and my job is to...
Metal building with living quarters the panel is on the outside and about 20 feet away from new build that will be 2x6 what type of shielded wire...
I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...