Search the forum,
Discuss Pumps /Controls in the UK Electrical Forum area at ElectriciansForums.net
K
karmannmann
Help I am working on a Biomass with District heating I have a 3phase pump for the boiler to accumulator and a single phase shunt pump these are straight forward enough I think. The head scratcher is: I have a 3 phase pump which delivers the heat to a heat exchanger in the properties and a single phase standard c h pump after the heat exchanger circulating round the property this pump will come on with a timer lifestyle or equiv I will need both this pump and the 3phase delivery pump to come on at the same time which is 100 metres away how would i wire in a contactor or any other ideas?
As tony says diagram please but to wire in a contactor you'll need 3 phase in the top,three phase out to pump the other side of the contactor and a means of activating the "coil" of the contactor,usually labelled A1 with A2 being return.
We need to know coil voltages,output voltage from switching device etc.
Also have you worked with three phase before?
Sorry Tony not very good when it comes to drawings and computers, Basically I have a programmable timer when it comes on the pump on the central heating will run but i need to send a signal to the other pump in the boiler house by relay to come on at the same time I know i will have to run a cable from the house to the boiler house but how do i wire this relay the pump in the boiler house is 3 phase.
Ive done a similar set up with the 2 pumps wired into the programmable timer but both were single phase.
Cheers
Karmannmann,you really need to know the coil voltage before you do anything fella,wiring it up is relatively straightforward as yes you do run a cable for the relay but if you get 5 core SWA you can do it through that.
Really need more details fella,have you got the relay details/pump etc.
Not being patronising but are you sure your experienced enough to do this?
Yes just not done much on this before. The pump GrundfosTP 32-150/2
0.31 L/s128 kpa
2865 RPMStainless steelCast Iron
40 C
10 Bar32 mm
0.37 Kw
50 Hz
3 x 220-240 D/380-415 Y V1.74/1.00A
490-530 %
Nothing on the relay yet but will find out.
Cheers
The way I see it is...there's a remote heat source with a 3P pump (Pump A) supplying a Local Heat Exchanger (HX) with several 1P pumps (Pump B,C,D...) serving each dwelling.
Some options to play around with:
1: Pump A runs continually keeping HX up to temp, Pump B kicks in on demand. Costly to run!
2: As 1, but HX has Hi/Low temperature sensors to control Pump A.
3: Pump A only kicks in when Pump B powers up, probably cheapest but there would be a delay while HX gets up to temp.
Not forgetting there is pump B,C,D,,,,,
I'm also not being patronising but it is obvious you aren't experienced enough to do this, and should have some on site professional help
Piggyback a relay (230V coil) across the CH pump, will give you a volt free contact. Bring control voltage from 3ph pumphouse through voltfree contact and back to 3ph pump contactor. Personally I would be considering some form of interlocking to make sure pumps are running correctly?
Reply to Pumps /Controls in the UK Electrical Forum area at ElectriciansForums.net
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Hello, I've been trying to find some information on split-phase today but not having much luck which brings me here. We're moving house to quite...
We have just completed a self build, and heating system is Air Source Heat Pump, unvented HW cylinder, Buffet Tank, all Vaillant equipment. The...
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...