Discuss Regulations around stairwell wiring in the UK Electrical Forum area at ElectriciansForums.net
Hi all,
I have two questions regarding wiring and containment on commercial property stairwells in Ireland.
We are currently wiring a 3 story pub-to-be. We plan on using plastic conduit- surface from top stairwell landing to the bottom landing. I can't find anything to the contrary in the regs about it, but it was remarked to me by the fire alarm guy today that we cannot use plastic conduit, as it is an emergency stairwell/escape route. He said it has to be steel conduit. I know fire alarm cabling and containment has to be steel or have steel supports or saddles. But what about electrical wiring?
Second question, relates to the same stairwell.
There are 3 doors leading onto the stairwell. Ground floor, 1st and 2nd floor. We will have lights on every landing, but to be brought on by a sensor when you come through each of the 3 doors, which will bring on all lights on the stairwell. At first I thought of looping the sensors from 2nd to 1st to GF and then from outgoing on GF to lights. Is there a better solution or a certain fitting you could recommend?
Thanks in advance.
I have no specific knowledge of EIRE regulations regarding this - there are some on here who do, I’m sure - however if this were U.K. mainland then it would indeed be the case that all cabling over escape routes requires metal support to prevent collapse. What that looks like is open to discussion - metal saddles over PVC conduit does arguably stop cables from falling if the conduit has melted, same as a metal P clip,
As for the light switches - sounds to me like a simple job of triggering a contactor and timer.
No doubt emergency lighting comes into it somewhere.
There is a huge cost implication between steel conduit and pvc.
Is there an architect involved? A specification to follow? I would reckon a fire risk assessment has been done, so ask the customer.
When I do this I wire such lights in FP200 white cable.
I usually buy 3 core and earth 1.5 FP 200 for lights as this lets me add photocells / sensors anywhere along the route and add in extra sensors at any point.
Make sure you buy decent sensors like Sentinel. I prefer to keep the lights and sensors seperate - I don't usually buy lights with built in sensors as the light may not be powerful enough to power many other lights.
It's not just metal support to prevent collapse, in escape routes the cable and containment must also meet requiems for being non-flame propagating and I'm sure plastic conduit meets this requirement.
Hi all,
Thanks in advance.
You could use fittings with microwave sensors in that way you don't need a seperated sensor on each floor and they wouldn't have to be on the same circuit, if that would make the install easier. As for the conduit, it doesn't have to be metal but plastic with metal saddles isn't the best look.
How about these?
Hi all,
Thanks in advance.
I would ask the fire alarm installer to justify his claim. That said, personally I think that metallic containment would be a better solution for all of the reasons mentioned in response to your post. But that's not to suggest that non-metallic containment would be in breach of any Rule.
Reply to Regulations around stairwell wiring in the UK Electrical Forum area at ElectriciansForums.net
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Hi All, I am rewiring my basement, which includes the stairwell that leads from the main floor kitchen down to the basement. Here is an idea of...
At long last my wife is getting her new kitchen and the contractor will be running 10 or so new circuits from a new sub panel. The sub panel...
I have moved back to my house i was born in some 60+ years ago. Most of the original house's electrical receptacles are 2 prong with the center...
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
5K
