DIYer question.

I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily accessible.

I need an additional socket in the garage - 13 amp max. The easiest and hopefully cheapest way to do this is to take a spur off the 32 amp cable.

How should I do this? I will need a junction box and 2.5 mm cable for the 13 amp socket, but how do I do this safely? So for example how can I ensure the 2.5 mm cable is isolated from power going to hob when its on? Recommendations on products would be good also.

Apologies if a daft question.

Thanks in advance.
 
Also remember the circuit has to be RCD protected for sockets, that is another reason for wanting a look at the CU so folks here can advise.

Another factor in England and Wales is new circuits, etc, are notifiable work under Part P of building regulations. It might be far better to see if anyone here work in your area and get it done by someone who is a member of the competent persons schemes like NAPIT, NICEIC, etc, for less hassle and greater safety.
 
Hi,

Two pics attached. The first shows the consumer unit next to boxed-in services. Directly above this is the living room.

All circuits for the CU go up into garage ceiling void and arent directly accessible. However, the grey cable coming from the CU and through the boxing-in is the hob supply.

The plan is to have a board covering the opening, which will contain modem/router, switch, smart home devices and hide ethernet cable going to rest of house.

Easiest is to take spur from hob supply. Otherwise its taking a spur from garage ring, which would involve a lot more cable/trunking as sockets that are on the ring (and aren't themselves spurs) are on other side of garage..

Most practical solution I think is to tap into the cable thats there. But please advise.
 

Attachments

  • consumer unit and project.jpg
    144 KB · Views: 50
  • onsumer unit.jpg
    237.3 KB · Views: 48
How should I do this?

You should not do this.

Leave the dedicated appliance circuit as a dedicated appliance circuit and connect socket outlets to a socket outlet circuit, either an existing one or a new one.

The plan is to have a board covering the opening, which will contain modem/router, switch, smart home devices and hide ethernet cable going to rest of house.

In my opinion this would be better off on its own circuit to reduce the impact from a fault. It would be less than desirable for the Internet connection and network to go off when the hob develops a fault.
 
You should not do this.

Leave the dedicated appliance circuit as a dedicated appliance circuit and connect socket outlets to a socket outlet circuit, either an existing one or a new one.



In my opinion this would be better off on its own circuit to reduce the impact from a fault. It would be less than desirable for the Internet connection and network to go off when the hob develops a fault.
Thanks for this Dave. Not thought that if hob has fault and trips circuit breaker then internet goes off.

But isnt this the case for any circuit?
 
Use the spare way assuming the busbar covers it but if not a new one can be obtained. Simple job for an electrician and they can notify Building Control.
 
I’m in Somerset. Drop me a DM if you’d like me to take a look (if you’re in the right part - big county!).
 
Thanks for this Dave. Not thought that if hob has fault and trips circuit breaker then internet goes off.

But isnt this the case for any circuit?
Also, in a previous property I had a cooker isolation switch with an integrated socket to plug appliances. In essence this is what I want to do, but without the isolation switch. What I dont get is why its OK for the switch and socket but not to do a spur.
 
Also, in a previous property I had a cooker isolation switch with an integrated socket to plug appliances. In essence this is what I want to do, but without the isolation switch. What I dont get is why its OK for the switch and socket but not to do a spur.
I have no idea why you want to do this when there is a spare way, none at all.
 
I have no idea why you want to do this when there is a spare way, none at all.
(1) I thought I needed an electrician to connect to CU and contact building folks. (2) I wanted to do it myself and keep costs to a minimum. (3) I thought there would be a simple solution given the proximity of the cable to the hob.

I do appreciate your input though.
 
What I dont get is why its OK for the switch and socket but not to do a spur.
Electrically they are different ideas.
In short, reducing cable size half way along a run requires adding extra protection which would be a right pain to implement in this situation. (Wrestling 2 x 6 sq mm wires that aren't quite long enough into a fused spur would be rather torturous)
I wouldn't even entertain doing it this way, when it's such a trivial matter to run it into a new MCB (~£3) in the consumer unit. A simple gland in the side, and off it goes.

I'd imagine you could find a sparks that would let you run the cable and leave a couple of meters of cable for him/her to test, connect, and do the required paperwork.
 
Also, in a previous property I had a cooker isolation switch with an integrated socket to plug appliances. In essence this is what I want to do, but without the isolation switch. What I dont get is why its OK for the switch and socket but not to do a spur.

The cooker switch incorporating a socket is a bit of a legacy item that we just haven't let go of yet. Years ago a single socket was all you needed for the 1 or maybe 2 small appliances you might have and so it made perfect sense to have that socket built in to the cooker switch. At that point in time the regulations were quite strict about the number of sockets allowed on a circuit.
Since then things have changed somewhat, someone came up with the idea of the ring circuit to feed multiple sockets for a start.

As for why the spur is not OK but the socket in the cooker switch is it is partly down to who you are asking. Most active members of this forum are professional electricians and so our answers are based in regulations, best practice and experience.
We have all experienced the ways in which your proposed spur can cause problems in the future, it could be minor issues like getting shouted at for turning someone's Internet off in the middle of a zoom meeting when you thought you were just turning a cooker off. Or it could be the burned out and melted mess we've had to fix because someone connected a bit of 2.5 into 32A circuit wired in 6mm.

If you ask the same question on a DIY based forum you will likely get a different answer, possibly even a step by step guide on exactly how it could be done (which is not permitted on this forum)

Ultimately would you rather take the advice of professionals who know or have experienced all the ways this could go wrong or the advice of someone who's done it a couple of times before and 'it hasn't gone wrong yet'
 
Electrically they are different ideas.
In short, reducing cable size half way along a run requires adding extra protection which would be a right pain to implement in this situation. (Wrestling 2 x 6 sq mm wires that aren't quite long enough into a fused spur would be rather torturous)
I wouldn't even entertain doing it this way, when it's such a trivial matter to run it into a new MCB (~£3) in the consumer unit. A simple gland in the side, and off it goes.

I'd imagine you could find a sparks that would let you run the cable and leave a couple of meters of cable for him/her to test, connect, and do the required paperwork.
Thanks will follow advice
 
The cooker switch incorporating a socket is a bit of a legacy item that we just haven't let go of yet. Years ago a single socket was all you needed for the 1 or maybe 2 small appliances you might have and so it made perfect sense to have that socket built in to the cooker switch. At that point in time the regulations were quite strict about the number of sockets allowed on a circuit.
Since then things have changed somewhat, someone came up with the idea of the ring circuit to feed multiple sockets for a start.

As for why the spur is not OK but the socket in the cooker switch is it is partly down to who you are asking. Most active members of this forum are professional electricians and so our answers are based in regulations, best practice and experience.
We have all experienced the ways in which your proposed spur can cause problems in the future, it could be minor issues like getting shouted at for turning someone's Internet off in the middle of a zoom meeting when you thought you were just turning a cooker off. Or it could be the burned out and melted mess we've had to fix because someone connected a bit of 2.5 into 32A circuit wired in 6mm.

If you ask the same question on a DIY based forum you will likely get a different answer, possibly even a step by step guide on exactly how it could be done (which is not permitted on this forum)

Ultimately would you rather take the advice of professionals who know or have experienced all the ways this could go wrong or the advice of someone who's done it a couple of times before and 'it hasn't gone wrong yet'
Thanks Dave. Very interesting. I'll stick to professional advice on this one. I've decided on dedicated supply from CU.
 
The cooker switch incorporating a socket is a bit of a legacy item that we just haven't let go of yet. Years ago a single socket was all you needed for the 1 or maybe 2 small appliances you might have and so it made perfect sense to have that socket built in to the cooker switch. At that point in time the regulations were quite strict about the number of sockets allowed on a circuit.
Just tried to do some history on this over a coffee and it's an 'interesting' mystery (wish Lucien was around, I bet he'd have known!).

The relevant British Standard today is BS4177:1992 (and is £138 to read, so that's not happening...) however it's predecessor from 1967 simply refers to the purpose of the socket as "an auxilliary circuit for other devices", rated up to 15A (allowing both formats of BS 546 round pin AND BS 1363). That was a revision of BS1833 from 1952 where the major change was a jump from 30A cookers to 45A cookers (so the concept of a 45A / 11kw cooker has existed now for nearly sixty years - nothing new!!). BS1833 appears to have been born from the legacy DC days of BS438: 1932, no versions of which seem to be online even in the BSi archives - however - the 1967 standard makes reference in the text to the much earlier 1932 version as having used BS 546 for the auxilliary circuit. As BS438 didn't exist until May 1934 one assumes there was a revision at some point.

The bottom line is that we've had an auxilliary circuit on cooker outlets for about a hundred years.

My guess........ As early electric kettles were around from the 1910's as the replacement for gas stovetop ones, logically if you could afford to have an electric cooker installed then you'd not need your gas stovetop kettle anymore but were used to the concept of boiling water at your stove - so you'd buy an electric kettle and it would need adjacent power.
 
Just tried to do some history on this over a coffee and it's an 'interesting' mystery (wish Lucien was around, I bet he'd have known!).
Alas, Lucian is missed so often :(

My guess........ As early electric kettles were around from the 1910's as the replacement for gas stovetop ones, logically if you could afford to have an electric cooker installed then you'd not need your gas stovetop kettle anymore but were used to the concept of boiling water at your stove - so you'd buy an electric kettle and it would need adjacent power.
That is my feeling, that if you had just had an electric cooker fitted then you would want an electric kettle but might not have many (if any?) spare 13/15A sockets already.

The 13A plug with internal fuse of course means it is not important if the supply is 16A or 45A, etc. Having a 15A unfused outlet off 30A/45A seems a risk though? Did the oldest has their own rewirable fuse just for the outlet?

For a new kitchen with lots of sockets there is no need for the cooker+outlet fixture, but for many existing kitchens that extra socket is handy!
 
Alas, Lucian is missed so often :(


That is my feeling, that if you had just had an electric cooker fitted then you would want an electric kettle but might not have many (if any?) spare 13/15A sockets already.
Even at members rates it's not worth the money to find out! Old pictures might reveal some clues?

My own thoughts on them are that they're actually a danger - normally fitted adjacent / 'behind/above' a hob, using them means either having a trailing flex or worse, an arm, stretching above a hob.
 
The 13A plug with internal fuse of course means it is not important if the supply is 16A or 45A, etc. Having a 15A unfused outlet off 30A/45A seems a risk though? Did the oldest has their own rewirable fuse just for the outlet?

Skip to 22 mins!! Yes - they had internal 15A fuses (although from what time in history I don't know - BS88 was 1967)

 
Last edited:
Even at members rates it's not worth the money to find out! Old pictures might reveal some clues?
Yes, BSI documents (in fact most of them) are a real rip-off!
My own thoughts on them are that they're actually a danger - normally fitted adjacent / 'behind/above' a hob, using them means either having a trailing flex or worse, an arm, stretching above a hob.
These days maybe, but on the older style with the back plate and (sometimes) high grill they had to be at the side which is sensible place.
 
BS88 dates back to 1919 or so. Just think how low 88 is compared to 1363 that dates to 1947 or so!
I thought that was only the larger / HV formats?? NOT an expert in this, just casual interest!
 
I thought that was only the larger / HV formats?? NOT an expert in this, just casual interest!
The earliest reference I saw was for LV cutouts, but I don't have any of the standards (no need, too high a cost for curiosity) to answer that.

Some day I will hopefully find the time to visit the British Library to take a look for free (sort of)
 
Alas, Lucian is missed so often :(


That is my feeling, that if you had just had an electric cooker fitted then you would want an electric kettle but might not have many (if any?) spare 13/15A sockets already.

The 13A plug with internal fuse of course means it is not important if the supply is 16A or 45A, etc. Having a 15A unfused outlet off 30A/45A seems a risk though? Did the oldest has their own rewirable fuse just for the outlet?

For a new kitchen with lots of sockets there is no need for the cooker+outlet fixture, but for many existing kitchens that extra socket is handy!
The cooker socket is also handy for when a fault trips the socket circuit, you can still make a cup of tea whilst pondering.
 
I’ll confess that I’ve always been lazy and taken testing figures via the socket. My defence is that if 1.5m of 6mm cable down to the cooker makes that much difference then things are already on very shaky ground.
 
I’ll confess that I’ve always been lazy and taken testing figures via the socket. My defence is that if 1.5m of 6mm cable down to the cooker makes that much difference then things are already on very shaky ground.
Ah! but thats where I have found cross polarity when doing an EICR (twice in about 20 years and thousands of tests......)
 

Reply to Taking a spur off cooker supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
298
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
1K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
700
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock