UKPN unilaterally moving cutout and meter

Discuss UKPN unilaterally moving cutout and meter in the UK Electrical Forum area at ElectriciansForums.net

mattg4321

-
Esteemed
Arms
Reaction score
2,046
Got a customer of mine, small sports club with a 3 phase supply. Rang me in a panic this morning. No power. Diagnosed supply problem over the phone. Said call UKPN

They found the problem. A damaged joint right on the boundary of the building. Almost half under it apparently. They’ve said they’re going to cut the cable there and move the cutout and meter to this point.

Can they do this? Means sports club have no power for now and have to pay me or someone else to urgently run a sub main a good 20m or more to get them back up and running.
Hate UKPN with a passion!
 
ESQCR 2020 says no, they can't do that as effectively it's removing a connection without due consultation
 
Bottom line here is that it's their equipment, not the installation. It's no different to if the damage was half a mile away.
 
Section 23 onwards, I think
 

Attachments

  • ESQCR2020.pdf
    115.8 KB · Views: 23
Is (was) the cutout and meter inside the building, as in not on an outside wall?
Has the building been extended over (what's now) UKPN/s supply cable?

If the cable runs under the floor slab UKPN are right not to reconnect, there may be damage on that or possibly in the future.

They aren't removing a connection without consultation, they are carrying out an emergency repair but whilst doing so they can only re-energise the supply in line with current standards and if they are happy there are no other or potentially no other faults.

Have they finished and left, have they discussed what else needs to be done?
 
"(2) Subject to regulation 29, a distributor shall at all times take all reasonably practicable
steps to avoid interruptions of supply resulting from his own acts."
 
I need to go and have a look really. Power is off for now! Think it’s probably due to them not wanting to connect to a cable that runs internally as the cutout is the other side of the building currently
 

Reply to UKPN unilaterally moving cutout and meter in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock