It is not uncommon here in the UK on TN-C-S supplies to see a portion of the neutral current flowing via bonding to service pipes that are bonded elsewhere on the system to another TN-C-S supply (or even directly in to the Earth).
Basically the pipes end up in parallel with the PEN (CNE, MEN, etc) conductor so share some current depending on the relative impedances.