Why is split RCD not appropriate for TT?
No, but this seems to be a regular occurrence where the OSG says something and it turns out it's not actually a reg. Is the OSG fit for purpose?
Not looked at an OSG for over 20 years your book of choice is BS7671.
I know that but OSG is supposed to be a bite-sized, easy reference for whats in the big brown book. Seems like the OSG talks a lot of gibberish.
Here's another one.
OSG page 61.
'Other than at the origin of the installation, every circuit...that may have to be isolated without interrupting the supply to other circuits should be provided with its own isolating device. The device must switch all live conductors in a TT system and all line conductors in a TN system.'
This basically says all breakers have to be double pole in a TT, no?
Yet you go to 132.15.201 which the OSG references and it says absolutely nothing about this.
No spark worth his salt is fitting split load boards these days IMO.
RCBO & SP is all I quote for.
Here's another one.
OSG page 61.
The DP main switch makes it compliant.
But that reg says supply side of the incoming device eg main switch. **** me these books are confusing. Someone should rewrite them in normal language, they'd make millions.
It does also mention the internal wiring I think. Says something about them being double insulated or
reinforced.
Only as it pertains to a pre-assembled board's link cables as far as i can see.
'Regulation 531.3.5.3.2.201 requires that where Class I enclosures are installed in installations forming part of a TT system and RCD protection is used on outgoing circuits, all live conductors on the supply side of the incoming device must have double or reinforced insulation'.
Taken from NICEIC website.
swaRRR,
Tart83,
TrueNAS JBOD Storage Server
