531.3.2 (ii)
It does say 'considered'.
The same reg also mentions split RCD though so i don't think it means RCBO's are required in residential premises.
'Regulation 531.3.5.3.2.201 requires that where Class I enclosures are installed in installations forming part of a TT system and RCD protection is used on outgoing circuits, all live conductors on the supply side of the incoming device must have double or reinforced insulation'.

Taken from NICEIC website.
For Class I enclosures in TT systems where RCD protection is used on outgoing circuits, double
or reinforced insulation of all live conductors (incoming cables, extension terminals, etc.) on the supply side of the
incoming device, e.g. main switch, shall be used. Insulated and non-metallic sheathed cables are deemed to meet the
requirements of double or reinforced insulation.

NOTE 1: When selecting equipment, consideration should be given to the assembly manufacturer's internal line interconnecting
cable links on the supply side of an RCD being insulated and non-metallic sheathed, or having reinforced insulation
or equivalent mechanical protection.

From the book.

Supply side of eg main switch is massively ambiguous imo.
 
The same reg also mentions split RCD though so i don't think it means RCBO's are required in residential premises.

For Class I enclosures in TT systems where RCD protection is used on outgoing circuits, double
or reinforced insulation of all live conductors (incoming cables, extension terminals, etc.) on the supply side of the
incoming device, e.g. main switch, shall be used. Insulated and non-metallic sheathed cables are deemed to meet the
requirements of double or reinforced insulation.

NOTE 1: When selecting equipment, consideration should be given to the assembly manufacturer's internal line interconnecting
cable links on the supply side of an RCD being insulated and non-metallic sheathed, or having reinforced insulation
or equivalent mechanical protection.

From the book.

Supply side of eg main switch is massively ambiguous imo.
You were asking about the main tails and argued that :-
Only as it pertains to a pre-assembled board's link cables as far as i can see.
I was merely pointing out that it does mention DI tails or reinforced insulation.
 
That quote though says that all individual circuits must have their own DP isolating device. Yet the regs don't mention it.

If that were the case would it mean that all the 1000s of consumer units that use mcbs are not compliant ?
 
The same reg also mentions split RCD though so i don't think it means RCBO's are required in residential premises.

For Class I enclosures in TT systems where RCD protection is used on outgoing circuits, double
or reinforced insulation of all live conductors (incoming cables, extension terminals, etc.) on the supply side of the
incoming device, e.g. main switch, shall be used. Insulated and non-metallic sheathed cables are deemed to meet the
requirements of double or reinforced insulation.

NOTE 1: When selecting equipment, consideration should be given to the assembly manufacturer's internal line interconnecting
cable links on the supply side of an RCD being insulated and non-metallic sheathed, or having reinforced insulation
or equivalent mechanical protection.

From the book.

Supply side of eg main switch is massively ambiguous imo.
It doesn't say required it suggests them.
 
You were asking about the main tails and argued that :-

I was merely pointing out that it does mention DI tails or reinforced insulation.
Nah i'm on about the load side of the main switch to the supply of the RCD's which is what the picture in OSG shows.
 
'Other than at the origin of the installation, every circuit...that may have to be isolated without interrupting the supply to other circuits should be provided with its own isolating device. The device must switch all live conductors in a TT system and all line conductors in a TN system.'

This basically says all breakers have to be double pole in a TT, no?

Yet you go to 132.15.201 which the OSG references and it says absolutely nothing about this.

The DP main switch makes it compliant.

I don't believe these two statements can be reconciled.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

swaRRR

Deleted account
Joined
Location
England
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Why is split RCD not appropriate for TT?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
79

Thread Tags

Advert

Thread statistics

Created
swaRRR,
Last reply from
Tart83,
Replies
79
Views
9,067

Advert

TrueNAS JBOD Storage Server

Back
Top