That quote though says that all individual circuits must have their own DP isolating device. Yet the regs don't mention it.

It does mention 'without interrupting the supply to other circuits'.
I'm sure it says somewhere “that provision may be made for isolation of a group of circuits by a common means”
 
531.3.2 (ii)
It does say 'considered'.
The same reg also mentions split RCD though so i don't think it means RCBO's are required in residential premises.
'Regulation 531.3.5.3.2.201 requires that where Class I enclosures are installed in installations forming part of a TT system and RCD protection is used on outgoing circuits, all live conductors on the supply side of the incoming device must have double or reinforced insulation'.

Taken from NICEIC website.
For Class I enclosures in TT systems where RCD protection is used on outgoing circuits, double
or reinforced insulation of all live conductors (incoming cables, extension terminals, etc.) on the supply side of the
incoming device, e.g. main switch, shall be used. Insulated and non-metallic sheathed cables are deemed to meet the
requirements of double or reinforced insulation.

NOTE 1: When selecting equipment, consideration should be given to the assembly manufacturer's internal line interconnecting
cable links on the supply side of an RCD being insulated and non-metallic sheathed, or having reinforced insulation
or equivalent mechanical protection.

From the book.

Supply side of eg main switch is massively ambiguous imo.
 
The same reg also mentions split RCD though so i don't think it means RCBO's are required in residential premises.

For Class I enclosures in TT systems where RCD protection is used on outgoing circuits, double
or reinforced insulation of all live conductors (incoming cables, extension terminals, etc.) on the supply side of the
incoming device, e.g. main switch, shall be used. Insulated and non-metallic sheathed cables are deemed to meet the
requirements of double or reinforced insulation.

NOTE 1: When selecting equipment, consideration should be given to the assembly manufacturer's internal line interconnecting
cable links on the supply side of an RCD being insulated and non-metallic sheathed, or having reinforced insulation
or equivalent mechanical protection.

From the book.

Supply side of eg main switch is massively ambiguous imo.
You were asking about the main tails and argued that :-
Only as it pertains to a pre-assembled board's link cables as far as i can see.
I was merely pointing out that it does mention DI tails or reinforced insulation.
 
That quote though says that all individual circuits must have their own DP isolating device. Yet the regs don't mention it.

If that were the case would it mean that all the 1000s of consumer units that use mcbs are not compliant ?
 
The same reg also mentions split RCD though so i don't think it means RCBO's are required in residential premises.

For Class I enclosures in TT systems where RCD protection is used on outgoing circuits, double
or reinforced insulation of all live conductors (incoming cables, extension terminals, etc.) on the supply side of the
incoming device, e.g. main switch, shall be used. Insulated and non-metallic sheathed cables are deemed to meet the
requirements of double or reinforced insulation.

NOTE 1: When selecting equipment, consideration should be given to the assembly manufacturer's internal line interconnecting
cable links on the supply side of an RCD being insulated and non-metallic sheathed, or having reinforced insulation
or equivalent mechanical protection.

From the book.

Supply side of eg main switch is massively ambiguous imo.
It doesn't say required it suggests them.
 
'Other than at the origin of the installation, every circuit...that may have to be isolated without interrupting the supply to other circuits should be provided with its own isolating device. The device must switch all live conductors in a TT system and all line conductors in a TN system.'

This basically says all breakers have to be double pole in a TT, no?

Yet you go to 132.15.201 which the OSG references and it says absolutely nothing about this.

The DP main switch makes it compliant.

I don't believe these two statements can be reconciled.
 

Reply to Why is split RCD not appropriate for TT? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
842
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top