It does say 'shall be used'.It doesn't say required it suggests them.
It does say 'shall be used'.It doesn't say required it suggests them.
It says residual current devices shall be selected to limit risk of unwanted tripping, and then goes on to list split load RCDs and RCBO's for consideration. It doesn't say RCBO's shall be used.It does say 'shall be used'.
Regulation 531.3.2 (Unwanted Tripping) now points out the use of RCBOs for individual final circuits in residential premises as a method to prevent unwanted tripping of such protective devices.It does say 'shall be used'.
'Other than at the origin of the installation, every circuit...that may have to be isolated without interrupting the supply to other circuits should be provided with its own isolating device. The device must switch all live conductors in a TT system and all line conductors in a TN system.'
This basically says all breakers have to be double pole in a TT, no?
Yet you go to 132.15.201 which the OSG references and it says absolutely nothing about this.
The DP main switch makes it compliant.
It makes it compliant with regard to isolationI don't believe these two statements can be reconciled.
Yes I did later I said 'suggested'.You said RCBO's were now required in residential installations.
Yes I did later I said 'suggested'.
And it should really say “Required”It does say 'shall be used'.
Thats what the thread was about why it's ok with rcbos and not ok using split rcds.NICEIC says you don't need a up front rcd
On TT main switch the rest of the board rcbo.
Where split consumer units are used with a separate double-pole main switch and 30 mA RCCBs to protect the final circuits, the interconnecting cables which connect the load side of the main switch to the supply side of the RCCBs must be provided with double or reinforced insulation to comply with Regulation 531.3.5.3.2.201.Thats what the thread was about why it's ok with rcbos and not ok using split rcds
Where split consumer units are used with a separate double-pole main switch and 30 mA RCCBs to protect the final circuits, the interconnecting cables which connect the load side of the main switch to the supply side of the RCCBs must be provided with double or reinforced insulation to comply with Regulation 531.3.5.3.2.201.
If this isn’t the case, this particular arrangement wouldn’t be suitable for TT installations because the interconnecting cables wouldn’t be provided with adequate fault protection. If the metal enclosure became live due to a fault, it would cause considerable inconvenience as RCCBs don’t have integral overcurrent protection.
A recommended consumer unit arrangement with RCBOs which is suitable for use on TT installations .
I have read the post, but some peapleMaybe a good time for you to read the complete thread, so as to avoid saying the same things
The same reg also mentions split RCD though so i don't think it means RCBO's are required in residential premises.
For Class I enclosures in TT systems where RCD protection is used on outgoing circuits, double
or reinforced insulation of all live conductors (incoming cables, extension terminals, etc.) on the supply side of the
incoming device, e.g. main switch, shall be used. Insulated and non-metallic sheathed cables are deemed to meet the
requirements of double or reinforced insulation.
It makes it compliant with regard to isolation
Every circuit that may have to be isolated without interrupting the supply to other circuitsevery circuit...that may have to be isolated without interrupting the supply to other circuits
should be provided with its own isolating device.
The device must switch all live conductors in a TT system
DP main switch meets requirement for swithcing of all live conductors. Perhaps I'm tired and unable to see what's in front of me, but how does this meet the requirement that every circuit be provided with "its own" isolating device?
That statement I think is the OSG interpretationevery circuit...that may have to be isolated without interrupting the supply to other circuits
should be provided with its own isolating device.
The device must switch all live conductors in a TT system
DP main switch meets requirement for swithcing of all live conductors. Perhaps I'm tired and unable to see what's in front of me, but how does this meet the requirement that every circuit be provided with "its own" isolating device?
Where are you getting this statement from? I've searched the regs and that wording isn't in there.That statement I think is the OSG interpretation
Isolation: 537.2
Every circuit / installation must be provided with a method of isolation from the supply. This isolation device should also be provided with a method to prevent unintentional or inadvertent reinstating (usually lockable).
In a TN-S or TN-C-S system it is not necessary to isolate / switch the neutral conductor providing that it is ‘reliably’ connected to Earth on the distributor's incoming supply side.
It’s worth remembering that semiconductor devices can not be used as isolating devices
“Provision may be made for isolation of a group of circuits by a common means”
Where are you getting this statement from? I've searched the regs and that wording isn't in there.
It doesn't say that on the link you provided, either. So where are you getting the quote from?![]()
Isolation and Switching Chapter 53 BS 7671
Key Points of… Isolation: 537.2 Every circuit / installation must be provided with a method of isolation from the supply. This isolation device should also be provided with a method to preven…the-regs.co.uk
Do you mean theIt doesn't say that on the link you provided, either. So where are you getting the quote from?
Yes you're using that quote as the basis for saying the quoted reg isn't 100% correct but the quote doesn't appear anywhere in the regs.Do you mean the
Provision may be made for isolation of a group of circuits by a common means, ?
Just thought I'd offer another perspective on this:With RCBO's the supply is via the busbar. It's in a fixed position so can't come into contact with the casing.
I can't find where it is and i haven't got the book, but it says:Yes you're using that quote as the basis for saying the quoted reg isn't 100% correct but the quote doesn't appear anywhere in the regs.
Yes you're using that quote as the basis for saying the quoted reg isn't 100% correct but the quote doesn't appear anywhere in the regs.
The same could be said for a dual RCD board.Just thought I'd offer another perspective on this:
The busbar is fixed, but uninsulated, in an enclosure containing a number of sleeved CPCs. Sleeving, I'm told, is for identification only and isn't officially rated as an insulator (though real world I'm pretty sure it does offer some level of insulation). Anyway, the uninsulated CPCs could make contact with the uninsulated busbar, resulting in a L-E fault that won't disconnect.
This makes me think that this risk for TT installations is possibly worse for an RCBO board, vs a dual RCD board, where the cables feeding the RCDs at least have proper insulation.
It doesn't, i've searched an electronic version of the regs and that's not in there.I can't find where it is and i haven't got the book, but it says:
“Provision may be made for isolation of a group of circuits by a common means, if the service conditions allow this”
The busbars would be RCD protected on the dual RCD board wouldn't they? But not for the RCBO board (this all assuming TT, and no upfront RCD)The same could be said for a dual RCD board.
Yep. My mistake.The busbars would be RCD protected on the dual RCD board wouldn't they? But not for the RCBO board (this all assuming TT, and no upfront RCD)
Just thought I'd offer another perspective on this:
The busbar is fixed, but uninsulated, in an enclosure containing a number of sleeved CPCs. Sleeving, I'm told, is for identification only and isn't officially rated as an insulator (though real world I'm pretty sure it does offer some level of insulation). Anyway, the uninsulated CPCs could make contact with the uninsulated busbar, resulting in a L-E fault that won't disconnect.
This makes me think that this risk for TT installations is possibly worse for an RCBO board, vs a dual RCD board, where the cables feeding the RCDs at least have proper insulation.
Like I said earlier, I'm a bit confused as to what part of the regs I'm saying is wrong ?It doesn't, i've searched an electronic version of the regs and that's not in there.
The reg i quoted was written verbatim from the book.
Yes you're using that quote as the basis for saying the quoted reg isn't 100% correct but the quote doesn't appear anywhere in the regs.
It appears to have moved in the 18th to 422.3.13:Like I said earlier, I'm a bit confused as to what part of the regs I'm saying is wrong ?
I only have the 17th edition green book to hand, but it's certainly in there.
537.2.1.2 : Provision may be made for isolation of a group of circuits by a common means, if the service conditions allow this
I stand corrected.It appears to have moved in the 18th to 422.3.13:
422.3.13Except as permitted by Regulation 461.2, every circuit shall be provided with a means of isolation from all live supply conductors by a linked switch or a linked circuit-breaker. NOTE: Provision may be made for isolation of a group of circuits by a common means, if the service conditions allow this.
I stand corrected.
So it's a case of EVERY circuit SHALL be provided with a means of isolation, except for when they aren't. And make sure you don't read the other contradictory rule about this in a completely different section of the book where it says each individual circuit must be individually switched. Clear as custard once again.
The more i read these books the more i think the IET aren't fit for purpose - contradictions, ambiguity, spelling errors abound. Even some of their very important equations needed for testing are wrong in the books.
No wonder the rest of the world laughs at our electrical practices.
Hey it's been a good discussion i think!But if everything was as clear as glass, there wouldn't be forums like this where gentlemen discuss these things in a friendly, happy manner.![]()
I stand corrected.
So it's a case of EVERY circuit SHALL be provided with a means of isolation, except for when they aren't. And make sure you don't read the other contradictory rule about this in a completely different section of the book where it says each individual circuit must be individually switched. Clear as custard once again.
The more i read these books the more i think the IET aren't fit for purpose - contradictions, ambiguity, spelling errors abound. Even some of their very important equations needed for testing are wrong in the books.
No wonder the rest of the world laughs at our electrical practices.
A more general point...The more i read these books the more i think the IET aren't fit for purpose - contradictions, ambiguity, spelling errors abound. Even some of their very important equations needed for testing are wrong in the books.
A lot of sense in that approach.A more general point...
It's very difficult to take the 'painting by numbers' OSG (which is a simplified set of rules that can be followed exactly to comply with BS7671) and then try and work backwards to BS7671. Trying to guess the full version from a particular method of complying is almost like trying to reverse engineer the regs.
I took a break from the industry during most of the 17th edition era, and hence fairly recently did an 18th edition course. I was actually strongly advised to NOT read the OSG until I'd passed the exam, as the layout and manner in which it sets out things is not conducive to learning the regs. I think it was good advice!
The brown book for all it's complexity is laid out in a certain structured way, and learning to think in terms of this structure is the best way forwards. So I guess what I'm saying is that should be where the focus goes.
(I'm far from an expert on the regs, but I believe I understand the structure and then it's a case of slowly filling in the blanks!)
this chap has made a very good point i hadnt thought of beforeThe busbars would be RCD protected on the dual RCD board wouldn't they? But not for the RCBO board (this all assuming TT, and no upfront RCD)