During an Eicr noticed the remote garage got an up & over metallic door.. the garage got its own CU & relevant RCBO’s… No incoming services only the newly installed Garage Door which is controlled by remote… would you consider a MPBC to it😂
 
I think the roller mechanisms on these (the tank style pulleys) are often plastic for this reason. Just do a continuity test from cpc to the door, see what you get.
 
Then it needs bonding. By definition of an extraneous conductive part.
It may not be, though. If the controller / motor unit is class 2 (which I'd wager it is) then it's not an extraneous part. No different to the now infamous crittal window scenario. In fact I'd go so far as to suggest that by bonding it you could be introducing a potential hazard where none previously existed.
 
It may not be, though. If the controller / motor unit is class 2 (which I'd wager it is) then it's not an extraneous part. No different to the now infamous crittal window scenario. In fact I'd go so far as to suggest that by bonding it you could be introducing a potential hazard where none previously existed.
Agree once again this topic always causes concern
MPBC if required would mean a TT system, it’s a report @ the moment & FI required
 
It may not be, though. If the controller / motor unit is class 2 (which I'd wager it is) then it's not an extraneous part
The motor is surely irrelevant, if there is a large lump of metal in contact with the ground (the frame of the roller shutter door) then it's most likely an extraneous conductive part (but would only require bonding if it's simultaneously accessible with any exposed conductive parts). There are other circuits in the CU, which may not be connected at the moment, but most likely will be at some point, probably including sockets.

It would be prudent to test it in any case.

For an EICR, I would suggest it's a C2 if it proves to be an ExtConPt.
 
The motor is surely irrelevant, if there is a large lump of metal in contact with the ground (the frame of the roller shutter door) then it's most likely an extraneous conductive part (but would only require bonding if it's simultaneously accessible with any exposed conductive parts). There are other circuits in the CU, which may not be connected at the moment, but most likely will be at some point, probably including sockets.

It would be prudent to test it in any case.

For an EICR, I would suggest it's a C2 if it proves to be an ExtConPt.
By that logic so is a garden gate!! My question remains - how, exactly, do you propose that this door is going to become part of an electrical circuit?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

cliffed

Arms
-
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
MPBC is it required
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
23

Thread Tags

Tags Tags
required

Advert

Thread statistics

Created
cliffed,
Last reply from
JK-Electrical,
Replies
23
Views
2,169

Advert

Back
Top