PME is not prohibited on a building site.Why?
That seems a bit severe unless it is a specific situation (building site, marina, etc) where connection to a PME style of supply is prohibited.
PME is not prohibited on a building site.Why?
That seems a bit severe unless it is a specific situation (building site, marina, etc) where connection to a PME style of supply is prohibited.
I think that’s an ish at best! So whilst 704.411.3.1 does not specifically prohibit it - outright - it does seriously discourage it, though. My view is that this Reg exists to allow PME supplies to be delivered to sites to get them going (with subsequent ‘normal’ deployment once construction is complete) but with the intent to not use the CNE aspect and make a TT instead. I also assume that as soon as the much discussed change to mandate foundation earthing systems comes into play then this Reg will disappear completely as irrelevant. Maybe. Just my take on it.PME is not prohibited on a building site.
Simultaneously accessible parts can be touched by a person, it’s internally & externally that could be the problem.Seeing industrial Roller Doors obviously these are actually attached to the main Metal Structure of the building which have a MPBC connected to it.By that logic so is a garden gate!! My question remains - how, exactly, do you propose that this door is going to become part of an electrical circuit?
Is the main building a metal structure?Simultaneously accessible parts can be touched by a person, it’s internally & externally that could be the problem.Seeing industrial Roller Doors obviously these are actually attached to the main Metal Structure of the building which have a MPBC connected to it.
Regulation 704.411.3.1 of BS 7671, whichPME is not prohibited on a building site.
Reply to the thread, titled "MPBC is it required" which is posted in Periodic Inspection Reporting & Certification on Electricians Forums.