During an Eicr noticed the remote garage got an up & over metallic door.. the garage got its own CU & relevant RCBO’s… No incoming services only the newly installed Garage Door which is controlled by remote… would you consider a MPBC to it
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss MPBC is it required in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
English man, English.consider a MPBC to it
Main Protective Bonding Conductor ..everything’s abbreviated these days…SozEnglish man, English.
Ok… it’s a bit different from normal circumstances, being a possible internal & external situation on fault conditionNo, unless it's likely to introduce a potential.
It’s in contact with the ground & the rollers are metal tooIs it in direct contact with the ground?
Then it needs bonding. By definition of an extraneous conductive part.It’s in contact with the ground & the rollers are metal too
It may not be, though. If the controller / motor unit is class 2 (which I'd wager it is) then it's not an extraneous part. No different to the now infamous crittal window scenario. In fact I'd go so far as to suggest that by bonding it you could be introducing a potential hazard where none previously existed.Then it needs bonding. By definition of an extraneous conductive part.
Agree once again this topic always causes concernIt may not be, though. If the controller / motor unit is class 2 (which I'd wager it is) then it's not an extraneous part. No different to the now infamous crittal window scenario. In fact I'd go so far as to suggest that by bonding it you could be introducing a potential hazard where none previously existed.
A bit of testing would be an idea to ascertain if it is indeed extraneous.Agree once again this topic always causes concern
MPBC if required would mean a TT system, it’s a report @ the moment & FI required
The motor is surely irrelevant, if there is a large lump of metal in contact with the ground (the frame of the roller shutter door) then it's most likely an extraneous conductive part (but would only require bonding if it's simultaneously accessible with any exposed conductive parts). There are other circuits in the CU, which may not be connected at the moment, but most likely will be at some point, probably including sockets.It may not be, though. If the controller / motor unit is class 2 (which I'd wager it is) then it's not an extraneous part
Why?For an EICR, I would suggest it's a C2 if it proves to be an ExtConPt.
By that logic so is a garden gate!! My question remains - how, exactly, do you propose that this door is going to become part of an electrical circuit?The motor is surely irrelevant, if there is a large lump of metal in contact with the ground (the frame of the roller shutter door) then it's most likely an extraneous conductive part (but would only require bonding if it's simultaneously accessible with any exposed conductive parts). There are other circuits in the CU, which may not be connected at the moment, but most likely will be at some point, probably including sockets.
It would be prudent to test it in any case.
For an EICR, I would suggest it's a C2 if it proves to be an ExtConPt.
Reply to MPBC is it required in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net