Hi, so I’m on a job currently and there’s no bonding to gas or water!

Gas isn’t an issue, as the meter is in the same cupboard and the consumer unit.

Water stop tap is on the complete opposite side of the house with no easy route without a fair amount of damage to decoration. Routing the cable around the property on the outside isn’t possible as it’s a mid terrace.

Any suggestions on what would be possible?

Is cross bonding from the gas pipes acceptable in the case?

Thanks
 
A gas pipe may not be used as a bonding conductor, so no.
Sometimes I have been able to route the cable into the loft and back down into the kitchen.

I assume you have checked that the water pipe is actually an extraneous conductive part?
 
I had one the other day, stop tap right at the back of the house and needed to do some kitchen electrics, bloke is saying be very careful with the incoming water pipe as its lead so don't bend it. I had a closer look to see where I could clamp onto and it was a black plastic alkathene pipe, luckily I hadn't ran 20M of bonding in yet.
 
Is CU and Gas under the stairs? Or in corner of front room, or over the front door?
Random ideas:
Cellar?
Floor void under ground floor?
Lift landing floor boards, through airing cupboard to loft, down back of house?
D-Line trunking, under kitchen cupboards?
 
Hi, so I’m on a job currently and there’s no bonding to gas or water!

Gas isn’t an issue, as the meter is in the same cupboard and the consumer unit.

Water stop tap is on the complete opposite side of the house with no easy route without a fair amount of damage to decoration. Routing the cable around the property on the outside isn’t possible as it’s a mid terrace.

Any suggestions on what would be possible?

Is cross bonding from the gas pipes acceptable in the case?

Thanks
I would really try and see where the water enters the house, to see if it is a blue plastic pipe, meaning no bonding required.
10 mins with an inspection camera could save you a lot of work.
 

Reply to the thread, titled "Bonding gas and water" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top