R1+R2 Calculations from ZS
My hair looks very much like lennys profile pic during live testing , spot on sintra just What i think
Thanks Guys, apparently we have to have a MWC, thought I was right about R1+R2 calcs, this web site is so good for scratching the head and finding info however trivial it may seem. Its a huge world of Electrical knowledge we have to have in our heads, we can't pretend to have all the answers.
Thanks Mickeysparks
Because when you measure Zs, you could have parallel paths (pipework etc.). When you measure R1 + R2 you should be measuring just the cable resistance, ie. conductors not terminated at a busbar.
So generally worst case Zs = Ze +( R1 + R2), and when you measure Zs it will probably be less (due to the parallel paths). Thats the theory anyway!
except for the aforementioned parallel paths, resulting in a lower Zs than from calc. from R1+R2. if you calc. using R1+R2+Ze, that will give you the expeced value of Zs. if you then measure Zs and get a higher value, that's when you start worrying what effect has the MCB and RCD on the result.
then you clip your green lead on to the armour/pipework
do you mean testing R1+R2 when due to containment being the cpc, you can't eliminate parallel paths?
mickeyspark,
telectrix,