View the thread, titled "DNO Issue !!!!" which is posted in Australia on Electricians Forums.
P
Ponty Massive
Started a PIR for a customer to find the Ze was 58 ohms on a TN-S supply. Contacted the DNO who sent out one of their "Engineers." He confirmed my reading and then called for a jointing team.
The jointing turned up and said they had a reading of 0.3 ohms.
I went back to the property today to find again a reading of 58 ohms???
Called them up and again they sent another engineer around. I waited 2 hours but couldn't wait any longer. Finally had a call from the customer 3 hours later saying the DNO guy had turned up and could I speak to him on the phone? I explained my reading to the guy and he said he was getting a reading on 0.3....
He asked my how I was doing my test? It's a very old supply but I explained the incoming live to the suppliers fuse had exposed wire, I tested between this, neutral and earth. He then said his meter only had two leads and he could only test between live and neutral or live and earth but could not do all three???
Anyway, he excepted my reading of 58 ohms and said he would call his office.
20 mins later I had a call from the customer saying the DNO would PME the supply for a cost of £140+VAT.
Is this right? Surely it's their responsibility to provide a satisfactory earth??
Any help apprreciated !!!!
What's testing a socket got to do with he's supply Ze?? All he would be seeing is Zs, that maybe acceptably low due to good earth paths from the Gas and Water bonds.
i ad something like this ze high they sent an engineer around tested one double socket got an acceptable reading and left
that wasn't an engineer, that was a monkey. like measuring the titanic's funnel, then saying the ship was OK.
As tony says if they provide an earth then they are under a legal obligation to maintain it. If they did not provide one or some cowboy has put an EC14 earth clamp around the paper lead incoming cable they will charge to supply a PME earth terminal.
OP why is it not ok for the DNO to use 2 wire testers??? When testing Ze they should remove the cutout fuse and customers earth and test L-N on concentric pvc supplies (PME, TN-C-S) and L-N and L-E on paper lead cables TN-S and (PME, TN-C-S). You do not need three wires to do this!
I've been on the phone most of the day trying to sort this out. Seems the house was built circa 1955, the DNO have finally revealed the supply is a TT and when the original installation was done to the house, the domestic electrician who did the wiring, simply put a clamp on the armourings and used it as a TN-S supply, obviously no testing was done or has ever been done (dispite the fact they had a conservertory fitted about 10 years ago with sockets, lights and outside supplies).
DNO suggested putting a rod in or they would PME for around £140+vat.
What also amazes me is, theres a sticker showing a new digital meter was installed in 2008!!!!!
What also amazes me is, theres a sticker showing a new digital meter was installed in 2008!!!!![/QUOTE]
People talk about DNO engineers being lets say less than thorough, well meter readers have in general less understanding of electricity than most
single cell amoeba. That may be a touch harsh but the amount of meter tails i have come accross that have just fallen out is quite shocking. FFS they only have about 4 connections to get tightened up correctly.
Could someone explain how using a 3 wire tester would give a different result for Ze. I have a 3 wire tester but only use 3 wires when I dont want to trip the RCD, if I'm measuring Ze I just use 2 wires.
Could someone explain how using a 3 wire tester would give a different result for Ze. I have a 3 wire tester but only use 3 wires when I don't want to trip the RCD, if I'm measuring Ze I just use 2 wires.
It is possible to get different readings by changing from a 2 wire to a 3 wire test on Ze or Zs.
Example from a real fault, (Megger 1552)
Tested a socket for Zs with plug, got a reading of 2.8ohm, tested another socket, 2.7ohm, maybe a broken ring or something? But continuity and readings OK on ring.
Go to another ring, high readings there as well.
Maybe Ze is high, so I did a two wire 20A bond test at the board, got a reading of .2ohm ish.
Strange I thought, get 2 wire Megger 345 no trip out, and do Z tests across the board all low readings?
Turn board off, do ohm test across MCB's check other circuits all OK?
Test across Neutral contact of double pole RCD and get 2 ohms ish FFS
Three wire testing uses the neutral as well.
Also on Hager RCDs and MCBs, always test for contact resistance they they burn easy, I have had around 5 cases of this.
Hope this helps.
On a Ze you should be testing L-N anyway!Really? I have installed hundreds and hundreds of Hager boards and never had or heard of anyone having a burned out main switch or breaker.Had a couple dodgy rcd's and that's it!You must be buying fake stuff
ombusdman are sill to get back to me about S.P.s extorsionate charge for fitting an isolator as they dont cut and reseal any more only fit isolators at £150 ffs I told them Id pay no more than £50 as 1 hr and £15 for isolator but they have monopoly
Reply to the thread, titled "DNO Issue !!!!" which is posted in Australia on Electricians Forums.