K
Kev2632
I was just wondering with the N-E being joined at the incomer, if i was to go downstream of a circuit which was "NOT" Rcd protected and tested between Neutral and Earth that would appear as a dead short between N-E is that correct? but if i was to go downstream of a RCD protected it wont be there is at that correct? as it cant get passed the RCD is that right?
Thanks.
Not quite, no. An RCD is basically a measuring device, not a physical barrier (until it trips), so the N that goes in is the same N that goes out. But what you will find is that the minute you try to test the principle it will trip due to various stray currents in the system.
Yea, but why doesnt the RCD see the neutral to earth that is present at the Service point then??
Because the rcd only monitors faults downstream to the device , not upstream towards the supply origin.
yea i know that, but why doesnt it see that the neutral and earth are joined then? as the N has gone to E?
It's not looking for (monitoring) N to E or L to E it's only monitoring L and N for missing current.
What goes up L must come back on N, if it differs by 30ma or more (or whatever the RCD rating) the RCD will trip.
N-E joined at the incomer of your house
Kev2632,
GLENNSPARK,