I was just wondering with the N-E being joined at the incomer, if i was to go downstream of a circuit which was "NOT" Rcd protected and tested between Neutral and Earth that would appear as a dead short between N-E is that correct? but if i was to go downstream of a RCD protected it wont be there is at that correct? as it cant get passed the RCD is that right?

Thanks.
 
Not quite, no. An RCD is basically a measuring device, not a physical barrier (until it trips), so the N that goes in is the same N that goes out. But what you will find is that the minute you try to test the principle it will trip due to various stray currents in the system.
 
Not quite, no. An RCD is basically a measuring device, not a physical barrier (until it trips), so the N that goes in is the same N that goes out. But what you will find is that the minute you try to test the principle it will trip due to various stray currents in the system.


Yea, but why doesnt the RCD see the neutral to earth that is present at the Service point then??
 
Because the rcd only monitors faults downstream to the device , not upstream towards the supply origin.
 
Last edited by a moderator:
yea i know that, but why doesnt it see that the neutral and earth are joined then? as the N has gone to E?

It's not looking for (monitoring) N to E or L to E it's only monitoring L and N for missing current.
What goes up L must come back on N, if it differs by 30ma or more (or whatever the RCD rating) the RCD will trip.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
N-E joined at the incomer of your house
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
56
Unsolved
--

Advert

Thread statistics

Created
Kev2632,
Last reply from
GLENNSPARK,
Replies
56
Views
5,317

Advert

TrueNAS JBOD Storage Server

Back
Top