Scenario: I was asked to replace a consumer unit in a house, rewireable to dual rcd. No previous problems. I did a visual inspection of the installation, did Zs'z on the rings, all was satisfactory. Changed the board, all circuits stable, and began to test. I've come across a break in the ring - no continuity on the end-to-ends.
Problem: the whole house (small victorian terrace) has the dreaded laminate flooring and the owners are not at all happy not at all happy not at all happy that I might have to get under their floors to find the break.
If the break is due to a wiring mistake then I can make to two 16A radials out of the mistake. If it's a mechanical break through the cable I should sort it out in case of exposed/extraneous conductive parts issues, although the stable rcds and mcbs would suggest this isn't the case.
1. Would you chaps be happy to go for the two 16A radials option?
2. Should I have done full tests on each circuit before I agreed to change it? As far is I know this is not required and I've never done this before.