H
highspark
Went to small job today. Fitting cooker to existing cooker point.
Before any connection
Done zs on circuit - tripped RCD.
Done rcd test no trip at 1x no trip at 5 x. This was on socket circuit aswell as cooker circuit.
Done ramp test. Ramped out at 33mA
Said cant install it. Circuit has failed.
Spoke to landlord. He said he'll send one of his sparks out. Got a phone call from other spark - nothing wrong with it.
Went back round to show him readings. He had dis board cover off and cooker socket case.Done exact same tests and everything was ok??????
What the hell went on there??
My meter is 6months inside calibration and was getting correct readings second time round. No trip on Zs all in tolerance on RCD tests.
Whats do you make of it?