I've just been flicking through the regs to do some cable calcs for a job and noticed that a 4mm 2 core cable installed using method B (under floors etc) has a capacity of 30A. However it is ok to connect to a 32A MCB for a radial socket circuit. Don't know if its just me missing something (which I'm guessing it probably is!) but that doesn't sound right. I'm looking at table 4D2A. I just can't figure it out!
 
Thanks for the reply. I know its fine but I'm just trying to figure out why it is regarding the regs.
 
I've just been flicking through the regs to do some cable calcs for a job and noticed that a 4mm 2 core cable installed using method B (under floors etc) has a capacity of 30A. However it is ok to connect to a 32A MCB for a radial socket circuit. Don't know if its just me missing something (which I'm guessing it probably is!) but that doesn't sound right. I'm looking at table 4D2A. I just can't figure it out!
If the cable is flat twin and earth how come you are using reference method B
 
installed under floors and buried in non-insulating wall ( e.g. plaster ) then ref. method C. then a 32A MCB is fine.
 
Hi there. I have exactly the same concern. I have 32A, 4mm radial circuit. The worst case reference method throughout the run is method B in conduit - more exactly I ran the cable in 20mm oval conduit chased into the brickwork - rather than capping (presumably capping not enclosing the cable is not termed as conduit). The tables showing 30A CCC (nearest table that the OSG is based on is multicore in BS7671, which makes me doubt how accurate the 30A figure is) I would expect that this fixing method is quite common. I'm not an experienced electrician so am interested what folk do in this case.
 
there is no reference method B for T/E. you can't downrate to 100,101,etc. as it's not in thermal insulation. i generally use ref. method C if some of the run is in trunking etc.
 
"there is no reference method B for T/E" ... yes I saw that. The OSG mentions this and claims the figures for 'multicore cable' are similar. OSG Page 52, Table 7.2 then gives method B for T&E @ 30A. Interesting to hear your experience though - so you run 4mm in conduit on a 32A CB? Cheers
 
you can run 4mm cable at 32A till the cows come home. it won't get anywhere near 70deg.C.
 
i would as long as the oval tube is big enough to leave a decent airspace. not if i have to use lube to get the buggers in. LOL.
 
That's interesting. I thought the airgap in conduit is what performs an insulating function. So I put the 4mm cables in 16mm oval conduit - not really tight, but not really loose,. Thanks for the reply...
 

Reply to the thread, titled "4mm radial circuit" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Thread Information

Title
4mm radial circuit
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
53

Thread statistics

Created
storyelectrical,
Last reply from
Engineer54,
Replies
53
Views
23,432
Back
Top