not if i have to use lube to get the buggers in.
I've just been flicking through the regs to do some cable calcs for a job and noticed that a 4mm 2 core cable installed using method B (under floors etc) has a capacity of 30A. However it is ok to connect to a 32A MCB for a radial socket circuit. Don't know if its just me missing something (which I'm guessing it probably is!) but that doesn't sound right. I'm looking at table 4D2A. I just can't figure it out!
What you planning on connecting to the cable? not a block of flats I hope haha, JK, How many sockets out of interest only?
read posts #7 , 9 & 11.
and cables under floors are nothing like as derated as conduit values.
why is it not fine ?
Yeah, why didn't I think of that, read replies that had not yet been written :dizzy2:
You should be a politician, answering one question with one of your own. LOL
The standard circuit A2 in the OSG does mention that the csa of the cables has to be assessed for CCC based on the installation method and the "informative" radial final circuit in the appendix of BS7671 also says that over current protection is not considered.
Because this is such a common circuit, it may well be installed incorrectly fairly often, but one can consider that domestic circuits almost never trip on overload and the likely current being carried will be far less than 30A so there is no significant danger, although as you say it will not meet the requirements of the regulations in many cases.
(copied my reply from the reference method explained thread)
This is a vain hope indeed!!!:nonod:The frustrating thing is the regs don't come out and say this - which is the sort of leadership I hoped the IET would provide.
Why don't you just use 6mm if you are concerned about it (that's what I'd do)?
I'm coming to the conclusion that if the layout of a house suits radial ccts then 20A, with 2.5mm is more flexible, just likely to be running one more cct. With 32A radial used sparingly, say for the kitchen. (Obviously if the layout suits ring then I would use ring)
Thanks for reply. Just out of interest, would you be happy, putting 4mm in oval conduit into a plastered wall, and clipping to joists, and then running on a 32A CB?Which is exactly what many sparks do these days. 20A radials for bedrooms, living room etc. and (personally) a 32A ring for kitchens, usually installed 'staggered'. I'd much rather work with 2.5mm anyway, much easier to terminate. 32A radials pretty easily fall below 32A CCC depending on installation method, and also because 4mm only has a 1.5mm CPC the circuit length is quite limited by Zs.
I'm coming to the conclusion that if the layout of a house suits radial ccts then 20A, with 2.5mm is more flexible, just likely to be running one more cct. With 32A radial used sparingly, say for the kitchen. (Obviously if the layout suits ring then I would use ring)