Sparkytlec
I usually use 4mm radials for socket but put them on a 20A o/c device and 2.5mm on a 16A. I haven't had a report of them tripping on overload either. It's very unusual for me to use a ring circuit these days to.
I usually use 4mm radials for socket but put them on a 20A o/c device and 2.5mm on a 16A. I haven't had a report of them tripping on overload either. It's very unusual for me to use a ring circuit these days to.
I thought about using a 4mm 32A radial once and came to the same conclusion as you. It only seems to be good for ref method C and I think there could be a problem fitting three 4mm conductors into accessories if you need to branch off at any point or modify the circuit at a later date, so I used a 2.5mm ring instead.
Thanks for reply. I suspect that it would be useful for the IET or similar to perform tests with T/E in installation method B, rather than using the multicore values in BS7671. I suspect the cable is JUST OKAY for 32A - although because it's on the limit I would use it sparingly when layout makes radial more suited in the kitchen. We really could do with one of the professional bodies carrying out the test and issuing a judgement - rather than loads of us wasting time/sleep wondering if we should downrate the CB. Cheers.
Perhaps if you disregarded BS 7671 when it comes to CCC of cables, and use the manufacturers data, you may find that your worries are totally unfounded!!
Why do you and it seems many others, need every situation documented in BS7671 (or by other bodies), it's never going to happen!! BS7671 is basically only a guide at the end of the day, your still expected to make your own educated decisions based on your electrical knowledge etc!!
Perhaps if you disregarded BS 7671 when it comes to CCC of cables, and use the manufacturers data, you may find that your worries are totally unfounded!!
Yeah, why didn't I think of that, read replies that had not yet been written :dizzy2:
You should be a politician, answering one question with one of your own. LOL
at the end of the day you can talk about the finer points of reference methods and ccc till the cows come home.
but 4mm under floors on a 32mcb works just fine , end of.
you either see that through experience or you get hung up on the regs because you lack said experience.
im happy to rely on my own engineering judgements that come with 20 years in the game , many others dont.
Perhaps if you disregarded BS 7671 when it comes to CCC of cables, and use the manufacturers data, you may find that your worries are totally unfounded!!
Why do you and it seems many others, need every situation documented in BS7671 (or by other bodies), it's never going to happen!! BS7671 is basically only a guide at the end of the day, your still expected to make your own educated decisions based on your electrical knowledge etc!!
If say the cable is 4 mm2 flex of diameter 11.6 mmThis is all assuming that 'under the floorboards' is method B.
What does 1.5De ≤ V < 50De mean?
where De is diameter of cable and V is height of space.
I can understand one side or the other but together it doesn't seem to make sense.
The trouble is, a lot of you old timers want to have your cake and eat it. Anyone who comes on here and says something that is against the regs, generally but not always, gets blasted and labelled a Electrical Trainee. Yet, when the forum Illuminati do it, we're just told to accept it as 'experience'.
At the end of the day, to coin your phrase, sticking to the regs never got anyone killed, so I find it strange that people would get criticised for doing so.
Cheers