R
rattlehead85
Doing an EICR on a church at the moment and found this board serving some lighting circuits within the chapels all wired in tinned copper imperial singles run through conduit used as cpc. The switch fuse feeding this board is located remotely at the intake position within another area of the church using an old style 30amp rewireable with porcelaine carrier. I have given this board a C3 departure as it has no local means of isolation either within the board or nearby and no labeling or indication of isolation point. Have i made the right observation on this or have i misinterpreted the regs here? 