Recent content by newfutile

  1. newfutile

    UPS - Earth - RCD what is required, and testing?

    If all the metal cases are connected with a cpc then 2 faults will trip fuses or circuit protection. Im not sure making your own TN type of supply would be allowed perhaps contact the manufacturer, its the same type of thing with small generators for burger vans and the like. The main danger...
  2. newfutile

    Bit of an odd one, one socket not working

    Either loose connections of a hidden fused spur,hope your removing all power while you Check these things?
  3. newfutile

    I need help with grounding.

    Busbars are usually live or hot as you say over there. I'm not sure what your electrical code says,but over here we would use a ground from a socket or take it back to the DB to the earth bar.
  4. newfutile

    Earth required or not on heat call wiring center

    Even if its not used every point should have a cpc
  5. newfutile

    New cooker still trips rcd. Boggling me.

    You really need a low amp clamp meter round the live and neutral,this will let you see where the leakage comes from,turn off all other Circuits on the shared (RCD). Idealy run each element on its own for 10 or more minutes
  6. newfutile

    This is a good'un!!!!

    I had a case like this where all the sockets (keyswitch) were wired L-N reverse from the manufacturer (we think). In this case if polarity is correct at the Consumer Unit a wander lead can be used to check L N E at each socket to the disconnected Consumer Unit cables
  7. newfutile

    "voltage relay" instead of RCD ?

    I don't think it's for earth leakage it appears to be to interrupt the power if it gets too high or low,I would try to get a proper rcd as well as that device
  8. newfutile

    Electric showers

    Shower priority unit,or a plumbing solution like a huge tank of hot water.
  9. newfutile

    Wagos/ connectors ?

    Wago are the best I think but ideal do some that are cheaper
  10. newfutile

    Ultrasonic cleaner??

    You can test it with aluminium foil
  11. newfutile

    Some questions around AFDDs

    You can fit Arc Fault Detection Device where you want not just sockets,some loads may not be enought to trip them,different makes show different patterns of lights,Hagar connects to an app to tell you the fault,though some have said bad things about the Hagar.
  12. newfutile

    5357 - College Design Calculations

    You Dont need to allow 13 amp per socket, just use either a standard ring 2.5 on 32 amp or a radial on a 16 amp 2.5, i would imagine its a wet area and will need suitable sockets and (RCD) Residual Current Device
  13. newfutile

    Signal interference for AICO detectors?

    House code all the alarms first,we had a situation of a whole street going off at 8 am many days, this was due to no house coding being done and 1 place over cooking there toast
  14. newfutile

    EICR question, OLD AC RCD- code 3 or no code?

    It's not the regs changing it's how the severity is coded, napit seem to be different to electrical safety first,at the end of the day the inspector does the coding,though they should be able to justify why the code was assigned.
  15. newfutile

    What's the best way to ground a Jackery Explorer 2000 Pro power bank ?

    wiring up the earth will do very little if anything as i doubt any of the live(s) will be referenced to earth making it a neutral. also because of this you should be wary about having many devices connected to it, especially if class 1 (metal) and within simultaneous touchable distance. maybe...
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Advert

TrueNAS JBOD Storage Server

Back
Top