I keep getting short circuit between live and earth. I can't work out wether this is normal or a genuine fault. Unfortunately I can't lower the floodlight to inspect further. Can only test at the bottom of the base. Can any one help?
If the IR test was at 250v and no higher it's fairly unlikely it's an MOV, the clamping voltages are usually higher than that unless they're the type sometimes used in telecommunications and RS232 and other comms systems.
Yep never heard of a MOV
not just me then Solo.
MOV's are used as lightning and surge protection all the way through the network from transmission lines to being internally installed in control panels and appliances. They come in a multitude of guises.
All these are MOV based protectors and they'll all give low IR reading with a megger tester set on a high test voltage.
[ElectriciansForums.net] Insulation Resistance of floodlights [ElectriciansForums.net] Insulation Resistance of floodlights [ElectriciansForums.net] Insulation Resistance of floodlights [ElectriciansForums.net] Insulation Resistance of floodlights [ElectriciansForums.net] Insulation Resistance of floodlights [ElectriciansForums.net] Insulation Resistance of floodlights
Many appliances have an internal filter circuit PCB which has MOV's on it amongst other things.
This is daft. We're 26 posts into a thread called "Insulation resistance of floodlights" and the OP still hasn't told us what the insulation resistance of his floodlight is. It could be anywhere between 0.14 ohms and 0.14 megohms, which is the same ratio as that between a pint of beer and 24 articulated tanker lorries of it.
0.14 ohms
OK, how are you measuring this 0.14 ohms?
Is the floodlight connected to the supply cable while you're measuring?
Is it connected in parallel with several other lights?
Where exactly are you connecting your test leads to?
What's the Zs of the supply at the base of the lamp column?
What type of lamp is it?
Reply to Insulation Resistance of floodlights in the UK Electrical Forum area at ElectriciansForums.net
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...