Two cables connected to mcb | Page 5 | on ElectriciansForums

Discuss Two cables connected to mcb in the UK Electrical Forum area at ElectriciansForums.net

Jay89

-
Arms
Joined
May 12, 2012
Messages
110
Reaction score
38
Location
Herts
Evening All

Im sure this will have been discussed at some point (if so please point me to a relevant thread)

I have been to look at some remedial work where a previous inspector has flagged up on multiple circuits 'DBx Cx has two cables in mcb, need separating - C2'

These circuits are either lighting or radial power circuits supplying a small amount of sockets. All suitably rated and with decent R1+R2 readings.

I have never seen this to be worthy of a mention let alone a C2 code, i have spoken to my CPS technical and they said they cant see an issue. Just looking for anyone else's opinion

Thanks in advance!
 
Sounds like there is a lot of lashing on going on.

@westward10, not arguing with your opinion on this but out of interest, someone used the principle above, say you were adding a light to an under stairs cupboard, where the consumer unit was and all cables coming out of the CU were buried and there are no spare ways. How would you do this?
 
If they wanted an additional socket in the cupboard, how would you feel about taking a spur off a RFC at the consumer unit?
Perfectly acceptable or incorporate into the ring final. A lot going on in this cupboard.
 
All you are doing is the following. Still one circuit as far as i'm concerned. How is this an issue?
[ElectriciansForums.net] Two cables connected to mcb
 
Well, well, well. Just look at the diagram below from an IEE Wiring Matters article. The diagram is taken from the IET Electricians Guide to the Building Regulations.
I think they have 2 radials in one MCB there or I could be seeing things.
Someone better notify the IET that their diagram does not comply with their regulations... :D

Right, thats put that one to bed. Now i'm off to bed...


[ElectriciansForums.net] Two cables connected to mcb
 

Reply to Two cables connected to mcb in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
778
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
769
  • Question
True. Although I'd hazard a guess that things like woodworm treatment are probably chemically quite similar? Don't know.
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top