Evening All

Im sure this will have been discussed at some point (if so please point me to a relevant thread)

I have been to look at some remedial work where a previous inspector has flagged up on multiple circuits 'DBx Cx has two cables in mcb, need separating - C2'

These circuits are either lighting or radial power circuits supplying a small amount of sockets. All suitably rated and with decent R1+R2 readings.

I have never seen this to be worthy of a mention let alone a C2 code, i have spoken to my CPS technical and they said they cant see an issue. Just looking for anyone else's opinion

Thanks in advance!
 
[ElectriciansForums.net] Two cables connected to mcb
...........
 
I note it on the certificate as for example in conductor sizes 3x1.5 3x1.0 and note that in some cases more than one conductor is terminated into one protective device and this is how it can be noticed.

I know a lot of people who C3 this
 
Don't recall suggesting it complied with BS7671 nor is it a personal view. I read Reg 314.4 that each final circuit should be given individual circuit protection that is it which I C3.

So 2 rooms with say 3 sockets in each room,

Each room fed from it's own mcb ok (1 conductor in mcb)
Both rooms wired on the same ring ok (2 conductors in mcb)
Room 1 wired as a radial with room 2 spurred from any socket in room 1 ok (1 conductor in mcb)
Both rooms on same circuit but wired independently back to the same mcb not ok (2 conductors in mcb)
 
Final circuit, and yes I will still C3 it lawyers or no lawyers.

You can't just state 'final circuit' without giving a definition for it.
How do you define what constitutes a final circuit and, crucially to this debate,what does not constitute a single final circuit.

At the moment it appears that your definition includes a requirement that a final circuit must only have one conductor at the ocpd.

If there is a 1' piece of cable connected from the ocpd to a JB and then two cables leave that JB to each serve two sockets, is that one circuit or two?
 
Don't recall suggesting it complied with BS7671 nor is it a personal view. I read Reg 314.4 that each final circuit should be given individual circuit protection that is it which I C3.

I read the reg exactly the same, it is not that reg which is at debate, it is the definition of a circuit.

If the two cables were not both serving sockets, lets say one feeds sockets and the other a pillar drill, then I would be inclined to agree with you. But when both cables are serving sockets, and if there is no overload as a result of the number of sockets, then I see nothing to comment on.
 
You can't just state 'final circuit' without giving a definition for it.
How do you define what constitutes a final circuit and, crucially to this debate,what does not constitute a single final circuit.

At the moment it appears that your definition includes a requirement that a final circuit must only have one conductor at the ocpd.

If there is a 1' piece of cable connected from the ocpd to a JB and then two cables leave that JB to each serve two sockets, is that one circuit or two?
See "definitions".
 
I read the reg exactly the same, it is not that reg which is at debate, it is the definition of a circuit.

If the two cables were not both serving sockets, lets say one feeds sockets and the other a pillar drill, then I would be inclined to agree with you. But when both cables are serving sockets, and if there is no overload as a result of the number of sockets, then I see nothing to comment on.
Your latter statement is somewhat contradictory and why you keep harping on about definition of circuit whilst it is the Reg to which I debate I have no idea.
 
As far as I'm concerned if you take two separate lighting circuits on two separate mcb's, and connect them together into one mcb then they become a single circuit. As long as the schedule and board are correctly labelled and identified there is no issue. It may be claimed that this could result in confusion, anyone confused by a correctly identified circuit consisting of two radials linked at the OCPD shouldn't be touching it in the first place.
 
The On Site Guide (page 71) says you can connect a non-fused spur from a ring final circuit "at the origin of the circuit in the distribution board", which I think would mean three conductors in the MCB and would look like a ring and a radial connected to the same protective device.

If spurring off a ring final inside a consumer unit is allowed then surely having a radial go off in two or more different directions from a consumer unit is ok as well.

What if you add a light or a socket in an under stairs cupboard near the consumer unit, surely you can connect that to an existing lighting or socket circuit in the consumer unit.
 
Your latter statement is somewhat contradictory and why you keep harping on about definition of circuit whilst it is the Reg to which I debate I have no idea.

What are you debating about the reg? The reg requires that each circuit be fed from a separate way. It does not make any mention of the number of cables which can be connected to an ocpd, merely the number of circuits.
In order to comply with this reg you must have a definition of what a circuit is, otherwise the reg is meaningless.

In definitions a circuit is defined as:
"An assembly of electrical equipment supplied from the same origin and protected against overcurrent by the same protective device(s)"
A final circuit is defined as:
"A circuit connected directly to current-using equipment, or to a socket-outlet or socket-outlets or other outlet points for the connection of such equipment."

Neither of these makes any mention of the number of cables which make up a circuit.
 

Reply to Two cables connected to mcb in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
281
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
791

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
769
  • Question
True. Although I'd hazard a guess that things like woodworm treatment are probably chemically quite similar? Don't know.
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top