Jay89

-
Arms
Joined
May 12, 2012
Messages
110
Reaction score
38
Location
Herts
Evening All

Im sure this will have been discussed at some point (if so please point me to a relevant thread)

I have been to look at some remedial work where a previous inspector has flagged up on multiple circuits 'DBx Cx has two cables in mcb, need separating - C2'

These circuits are either lighting or radial power circuits supplying a small amount of sockets. All suitably rated and with decent R1+R2 readings.

I have never seen this to be worthy of a mention let alone a C2 code, i have spoken to my CPS technical and they said they cant see an issue. Just looking for anyone else's opinion

Thanks in advance!
 
I would C3 it, two final circuits require individual circuit protection.

It's not two final circuits, it is one, the definition of a circuit in bs7671 is very clear on this.

What basis do you have for a C3? What is the improvement that can be made? Unless this Mcb is overloaded, which is a separate matter, then nothing is improved by splitting it in to two circuits
 
I suspect this is the case of an existing circuit and then someone lashing another to it because they cannot be be bothered to employ correct installation methods by using an additional protective device at a spare way or advising the existing board has inadequate capacity.
 
I suspect this is the case of an existing circuit and then someone lashing another to it because they cannot be be bothered to employ correct installation methods by using an additional protective device at a spare way or advising the existing board has inadequate capacity.
There are multiple consumer units in this EICR where it has been flagged, from what i can see most seem to be part of original installation (same cable and paired dressing). Mostly on three phase boards with no spare ways.
 
I suspect this is the case of an existing circuit and then someone lashing another to it because they cannot be be bothered to employ correct installation methods by using an additional protective device at a spare way or advising the existing board has inadequate capacity.

Based on what evidence? Whilst this is possibly what has happened, there is nothing in the regulations to prevent a circuit being extended in this way.
If a radial socket circuit has the capacity for additional sockets, then why not extend it from the DB if that's the most logical place to connect it? Surely this is better than adding an additional joint into the circuit somewhere?
 
reg 314.4
when an installation comprise more then one final circuit .each final circuit shall be connected to a separate way in the distribution board .

Yes, now add the definition of a circuit.

There is nothing which prevents a circuit being formed of two branches from an ocpd. This could be a better design if it reduces th overall length of the circuit
 

Reply to Two cables connected to mcb in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
281
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
791

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
769
  • Question
True. Although I'd hazard a guess that things like woodworm treatment are probably chemically quite similar? Don't know.
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top