HI all,

just need clarification on bonding of a mains cupboard please.

Setup is
Mains cupboard 2mtrs wide and 6mtrs long
10 cutouts feeding 10 flats , has meters then tails to cutout then 25mm concentric to each flat

5 water tanks are in there and cables from flats feed the immersion heaters, cooper pipes from tanks then above ceiling all plastic, also plastic feed coming in.

lighting and power in main cupboard off 5x5 split board all rcd, with PV inverter, and aerial boosters.

company has come in and said all the cooper needs bonding, its all plastered now so I think they might be assuming that all the installation is in copper but its not, I haven't bonded as I usually don't need to , but think that the cupboard is so narrow you can touch the cutouts (non RCD) and the copper of the water tanks, just need some guidance please .

Cheers
Grand
 
HI all,

just need clarification on bonding of a mains cupboard please.

Setup is
Mains cupboard 2mtrs wide and 6mtrs long
10 cutouts feeding 10 flats , has meters then tails to cutout then 25mm concentric to each flat

5 water tanks are in there and cables from flats feed the immersion heaters, cooper pipes from tanks then above ceiling all plastic, also plastic feed coming in.

lighting and power in main cupboard off 5x5 split board all rcd, with PV inverter, and aerial boosters.

company has come in and said all the cooper needs bonding, its all plastered now so I think they might be assuming that all the installation is in copper but its not, I haven't bonded as I usually don't need to , but think that the cupboard is so narrow you can touch the cutouts (non RCD) and the copper of the water tanks, just need some guidance please .

Cheers
Grand
May help you
 
I think by chance they may be close to being right. Essentially the water tanks and exiting copper pipes are almost certainly not capable of introducing an earth potential. However if the flats have been designed as individual installations then, because of the wiring from the flats coming back into a communal area, a fault potential from one of the flats could be introduced into the cupboard via the immersion heaters. This is the uncommon situation of an extraneous conductive part introducing a potential that is not earth potential. (extraneous to the cupboard, not the flat)
Working against this is that the flats earthing systems are all commonly connected via the incoming earth and (assuming you meant split concentric rather than a non compliant concentric) at bonding suitable sizes so the fault potential will transfer to the other flats anyway, however only via the volt drop over the immersions cpc which may mean an elevated voltage when referenced to the other tanks.
All this does depend on whether the design has been done as one conjoined installation or ten different installations, though if there is no other bonding it is difficult to define and it is a bit blurred by having the flat circuits all coming back to the common area.
It is a bit like if you installed a metal clad socket from your CU into your neighbours house and both were fed from the same supply, a fault on that socket could mean a shock risk to the neighbours even though the socket is earthed back to your house.
[ElectriciansForums.net] Bonding of main cupboard
 
If there is no gas at the property and therefore I assume electric heaters not radiators, then overall with the interaction of all the circuits, aerials and PV being mixed together and assuming there are no large exposed structural metal parts that are not common to all flats then I think that perhaps the whole structure can be considered as one installation. It does not seem sensible to try to claim that each flat is an enclosed area not interacting with other flats. Therefore each tank is an exposed conductive part as it is part of "the" electrical installation and requires earthing, which is presumably in place.
I did do a calculation with some random figures and came up with one tank being 140V above the others in a fault situation, but I cannot see how this would differ from a metal light fitting in a house above an immersion tank when the immersion fails to earth.
Just some thoughts.
 

Reply to Bonding of main cupboard in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

L
  • Article
Possible airlock We have a sink, washing machine and shower in a ground floor utility room. Cold water is supplied from a loft tank. This...
Replies
0
Views
158
Lightup
L
By the time you've dealt with isolator valves that won't shut off and drain valves that won't open, half a day will be gone before you've removed...
Replies
5
Views
751

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Thread starter

Joined
Location
Midlands
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Bonding of main cupboard
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11
Unsolved
--
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top