Regarding the above regulation, it is now a requirement that in the event of a fire ALL wiring systems now need to be designed and installed to ensure they do not prematurely collapse thus put lives at risk be it of the general public or that of the emergency services.

I want to just open a discussion on why the IET has failed to mention the use of plastic rawl plugs or similar fixing as it has been shown that they fail under test conditions, also to discuss the alternatives given that we are looking at a possible steel plugs as a option. Now it is my believe that you only need to ensure support at intervals and in between standard fixings are acceptable as long as the fire rated supports can carry the weight without the standard fixings given these may fail.

I am now designing jobs to start in the new year and will be complying to the 18th so just wondering who out there is both aware and has a good cheap solution?
 
Last edited:
We did have a thread where we discussed this.
I'll see if I can find it....
 
even screwfux can supply these'
https://www.NoLinkingToThis/p/rawlplug-metal-wall-plugs-6-x-32mm-50-pack/958
maybe use 1 in 3 fixings.
 
I did go looking for options when this first cropped up.

There's obviously the D-Line clips that go in trunking. For plastic conduit use metal saddles and possibly fix them to the wall with something like Walldogs which don't need a wall plug.

There's the good old fashioned buckle clip, but again you'd been needing to secure it with something that won't fail (possibly Walldogs, although I suspect the head of the screw may be a bit big).

P-Clips... same issue as above.

I did find these:-

Linian 1LCR608 Fire Rated Cable Clip 6-8MM - Red - https://www.thesafetycentreshop.co.uk/linian-1lcr608-fire-rated-cable-clip-6-8mm-red

Which look quite neat, just drill a hole and insert them. Not sure how practical they'd be for say a single cable.

But it's yet another grey area as there isn't really a definition of 'premature'. How long do the supports need to last? What about plasterboard on ceilings? Will that be good enough?

Which leads on to where do we stand with cables in floor/ceiling voids that you can't access for example? I've just done a job where I can't access long stretches of the void, so the cables are just laying in there. Are we expected to tell the customer we're going to have to tear down a partition wall so we can properly fix the cables in place? Can't see many of them going for that personally :rolleyes:

As for why they haven't explicitly mentioned rawl plugs... I suspect they would argue they don't need to because their wording encompasses all possibilities. If it could collapse, you shouldn't use it as the sole means of support.

Regards your belief you only need support at intervals... I concur. I believe Note 3 clears this up. "This regulation precludes, for example, the use of non-metallic cable clips or cable ties as the sole means of support where cables are clipped direct to exposed surfaces or suspended under cable tray, and the use of non-metallic cable trunking as the sole means of support of the cables therein."
 
What about plasterboard on ceilings? Will that be good enough?

Which leads on to where do we stand with cables in floor/ceiling voids that you can't access for example? I've just done a job where I can't access long stretches of the void, so the cables are just laying in there. Are we expected to tell the customer we're going to have to tear down a partition wall so we can properly fix the cables in place? Can't see many of them going for that personally :rolleyes:

A standard plasterboard ceiling & walls provide a 30 min barrier. I've not looked at document B, but I'm led to believe that cables in those voids, negate the need for fireproof fixings, as per the said reg being discussed.
 
I've advised my wholesaler to talk to Linian. Their clips can be used with cable (including SWA, replacing plastic cleats) and conduit. Spoke to them at Coventry Elex, they reckon they'll have grey clips (for T&E) by the new year.

Not tried them yet myself; at the moment I'm using the D-Line U-clips over doors, and metal saddles on PVC conduit, but neither are ideal visually.

Spoke to Q-Crimp at Elex too (whose T&E clips I favour), they said, "we'll have something available in the new year." It seems many of the manufacturers would have appreciated a bit more notice on this...
 
Anyone found custom designed replacements for plastic SWA cleats without resorting to the bodge of all purpose banding ?
@Andy78 @SparkyChick are these sort of thing you are thinking of? not sure on the pricing? but would almost certainly satisfy the new regulations?
Metal Cable Cleats | For Single, Multicore & Trefoil Applications | CMP - https://www.cmp-products.com/cable-cleats/product-range/metallic-cable-cleats/

EDIT
Just realised you all already had the same thought! The helios cleats are good though, Have used them in a garage before. Not sure on price as they were supplied with the equipment I was installing.
 
Last edited:
@Andy78 @SparkyChick are these sort of thing you are thinking of? not sure on the pricing? but would almost certainly satisfy the new regulations?
Metal Cable Cleats | For Single, Multicore & Trefoil Applications | CMP - https://www.cmp-products.com/cable-cleats/product-range/metallic-cable-cleats/

I suspect no on the CMP ones because of price, they are stainless steel, but I've not been able to find that many alternatives.

One cheap and nasty option may be to put a length of all-band inside a cleat, but getting the holes to line up would be a mare, but then maybe do that every other cleat and just stick to using plastic. Wouldn't be too hard for the manufacturers to include a spring steel band in the cleats themselves, that would solve a lot of the problems straight off.
 
I would also heed caution on choosing aluminium as a fixing choice, as I understand it the fixings have to withstand temperatures that fall within a range that would greatly reduce aluminium's structural integrity, I cannot comment about aluminium alloys as that would depend on what it made up of.
I see some of these fixing companies have opted for aluminium so possibly a chat to there technical support wouldn't go amiss if that becomes your weapon of choice.
 
This is the thread I was talking about.
Should have posted it sooner but the daughter wanted me to play Minecraft with her...
 
I think if your worried about plastic wall plugs failing the surrounding structure will have failed anyhow.
I don’t buy into the fact that you can’t use them at all to be honest.
I need more information to be sure tho
Your wish is my command
 
Just as an observation I have used linian fire clips and they are spot on and meet the 18th edition but also agree with people on here that by time rawl plugs fail the building would be down anyway.
 
@ elecshow the niceic did a talk aboit 18th and stated plastic rawl plugs are ok. So not sure why youve got a problem them. They are embeded into the fabric of the building by the time they melt and give way the buiding will be in a terrible state!
 
Regarding pastic plugs...

From the PDF report on the link in #21, page 10:

Similar to the first experiment, all the plastic clips on each lintel failed, resulting in the cable dropping down. A new observation from this experiment was that the supports in the centre of Lintel 2 had dropped out of the lintel. This was not a failure of the support but rather a failure of the plastic plugs used for fixing the supports to the lintel.

Page 12:
The findings from the short fixings study show that combustible wall plugs in concrete substrates demonstrate signs of weakening of mechanical strength from 300°C and above and that these fixings can fail at 400°C after up to a one hour exposure in controlled conditions.
[ElectriciansForums.net] New cable support regulation 521.10.202 (18th)

Of course, I'm just picking and choosing bits of the report, it's a bit lengthy but gives a fuller picture.
 
I have a close friend who lost at least one colleague as a result of entanglement due to a collapsed wiring system.

I've been lucky enough to be able to go on an industrial chemical plant training exercise with crews from Lancashire Fire and Rescue Service. If you've never tried on fire fighting gear, trust me we should be doing everything we can to minimise the chances of our work killing another fire fighter (or anyone else for that matter). Even on a cool night, it was stifling, heavy and limited my movement somewhat. I can't imagine the panic of not being able to see what's going on, trying to get yourself out of it.

Don't forget in some situations fires can be directed jets of combustible materials that could potentially create localised heating in the building structure.

They have made changes and crews are being issued with wire cutters, but surely it's better to try and ensure they never need to use them?
 

Reply to New cable support regulation 521.10.202 (18th) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
491
Yes looks like you are right! Though to be fair, AMD 1 only had EV stuff in it, so probably didn't change anything to do with testing? Still if...
Replies
4
Views
2K
  • Question
I'm glad you did...a piece of social history is always interesting!
Replies
21
Views
5K
Depending on the size of the company, ie, has a H&S department or H&S. I'd just use the phrase that's it's not compliant with BS standards and...
Replies
48
Views
10K
Heh, thanks ^^ Been browsing a bit the forum and there's a lot of interesting content. Hope I can stay for long.
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks