Hi all
Odd one today .. all 6 Hager rcbo's in a tn+n db have the test buttons not working..
But when tested with a multifunctiontester they react fine..
Now..I guess I'm going to have to fail them..even though they work fine.
Hager technical say they have never heard of this.
Db is in a plant room with a raised ambient temperature but not hugely ..say 36c .. rcbos are 2 x 6A B 30ma 2 x 20A C 30ma and 2 x 32A B 30ma .. fitted in 2014 by the looks of it.
All connections are good..fly leads good..circuit's are just for sockets and lighting..standard stuff.
Anyone had this before..
Any ideas

Ta
Vito
 
In essence, the test button just connects a resistor to create an artificial imbalance. Resistors have tolerances and temperature ranges. Could be the raised ambient has damaged them or is causing them to pass less current than expected.

Might be worth ramp testing them as well. If they are running slightly high and the test current created by the test button is slightly low???
 
Did you try the test button again after you're test with the meter? Seen it before where they haven't worked before proper testing but where fine after. (Not necessarily hager though)
 
Ramp tested fine 23 mA 25mA normal sort of range to me.
Just found it amazing that it was all 6 ..

As you say, the fact six have gone...

Is it humid where they are? Is it an IP rated board?

Could be the switch contacts are screwed due to environmental factors.
 
Yes I've had that before .. but then the rcbo or rcd didn't work at all .. these work fine with an auto test .. circuit's still connected .
 
I find Hager RCD devices some of the most reliable out there. I have however, as Murdoch says, had them not trip with the test button when connected N-E faults have been present.
 
As you say, the fact six have gone...

Is it humid where they are? Is it an IP rated board?

Could be the switch contacts are screwed due to environmental factors.

Yep .. this was my guess.. plant room ..2 commercial boilers 3 big water tanks .. all dry in there now .. but they have had multiple problems in there over the past few years..
Just the test button contacts have had it..?
 
I'll have to go back with my leakage clamp meter and check it out .. customer would be a tad unhappy to buy 6 new ones ....that also didn't work.
 
Yep .. this was my guess.. plant room ..2 commercial boilers 3 big water tanks .. all dry in there now .. but they have had multiple problems in there over the past few years..
Just the test button contacts have had it..?

Could be.. but I'm just floating ideas around. I've had to replace a CU locally that was in a domestic swimming pool plant room. Was in a right state, some MCBs wouldn't turn off, contacts were all corroded or affected by chemicals.

To avoid it happening again, I put a plastic unit, inside an IP rated steel cabinet, with every cable properly glanded through the cabinet.
 
Hi Vito - assuming they have the functional earth lead, perhaps check it's still connected. I don't really see how this could cause it, I'm just thinking out loud. :)
 
I find Hager RCD devices some of the most reliable out there. I have however, as Murdoch says, had them not trip with the test button when connected N-E faults have been present.

Andy, would that be because some of the created test current flows back through the neutral side of the sense transformer and then down the CPC resulting in less than the expected test current appearing on the sense winding?
 
Are these the type with a functional earth flying lead (cream coloured?)

Is this properly terminated to a known good earth. me too just floating ideas..
 
I think I have an answer
[ElectriciansForums.net] Rcbo test buttons not working - but works ok when tested
the test button leaks from phase 1 to phase 2.

Try ramp testing between those two phases rather than to earth and see what happens (assuming your RCD tester is good for 400V)

I bet there is either an imbalanced load (in favour of phase 2 or 3), or there is an imbalance in favour of 1 and a N-E fault. This is assuming the RCD tester leaks to earth from phase 2 or 3.
 
Yes there are 2 tp mcb's on the other side .. it's a 4 way tpn db.
The rcbos in question are single phase .. just incase anyone was thinking otherwise .
Yes rcbo's with cream fly leads .
Good shout though leesparkykent could well just switch all other circuit's off and check the rcbo's 1 at a time..
Ill report back when I know more.
Seems though from the replys that no one has had a non working test button on a working rcbo..
Bit novelty. ..must get out more!
Ta all
Vito
 

Reply to Rcbo test buttons not working - but works ok when tested in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
843
  • Question
Hi, No RCD was not ramp tested. At the time Fusebox was updated to RCBOs in 2021 the reading for both lights upstairs and lights downstairs was...
Replies
8
Views
3K
  • Question
That's exactly what I meant to say. 😆 Although quite a lot of the RCBOs now don't have the functional earth leads.
Replies
3
Views
2K
  • Question
I have the same SPD-RCBO unit that you have and mine came with a Busbar that connected up all 4 output terminals (x2 Live and x2 Neutral) at the...
Replies
11
Views
3K
  • Question
😚 Any Schneider breaker with iKQE on it is Square D compatible. Many others are too.
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks