Rcbo test buttons not working - but works ok when tested | on ElectriciansForums

Discuss Rcbo test buttons not working - but works ok when tested in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Joined
Nov 30, 2009
Messages
277
Reaction score
25
Hi all
Odd one today .. all 6 Hager rcbo's in a tn+n db have the test buttons not working..
But when tested with a multifunctiontester they react fine..
Now..I guess I'm going to have to fail them..even though they work fine.
Hager technical say they have never heard of this.
Db is in a plant room with a raised ambient temperature but not hugely ..say 36c .. rcbos are 2 x 6A B 30ma 2 x 20A C 30ma and 2 x 32A B 30ma .. fitted in 2014 by the looks of it.
All connections are good..fly leads good..circuit's are just for sockets and lighting..standard stuff.
Anyone had this before..
Any ideas

Ta
Vito
 
In essence, the test button just connects a resistor to create an artificial imbalance. Resistors have tolerances and temperature ranges. Could be the raised ambient has damaged them or is causing them to pass less current than expected.

Might be worth ramp testing them as well. If they are running slightly high and the test current created by the test button is slightly low???
 
Did you try the test button again after you're test with the meter? Seen it before where they haven't worked before proper testing but where fine after. (Not necessarily hager though)
 
Yes I've had that before .. but then the rcbo or rcd didn't work at all .. these work fine with an auto test .. circuit's still connected .
 
I find Hager RCD devices some of the most reliable out there. I have however, as Murdoch says, had them not trip with the test button when connected N-E faults have been present.
 
As you say, the fact six have gone...

Is it humid where they are? Is it an IP rated board?

Could be the switch contacts are screwed due to environmental factors.

Yep .. this was my guess.. plant room ..2 commercial boilers 3 big water tanks .. all dry in there now .. but they have had multiple problems in there over the past few years..
Just the test button contacts have had it..?
 
I'll have to go back with my leakage clamp meter and check it out .. customer would be a tad unhappy to buy 6 new ones ....that also didn't work.
 
Yep .. this was my guess.. plant room ..2 commercial boilers 3 big water tanks .. all dry in there now .. but they have had multiple problems in there over the past few years..
Just the test button contacts have had it..?

Could be.. but I'm just floating ideas around. I've had to replace a CU locally that was in a domestic swimming pool plant room. Was in a right state, some MCBs wouldn't turn off, contacts were all corroded or affected by chemicals.

To avoid it happening again, I put a plastic unit, inside an IP rated steel cabinet, with every cable properly glanded through the cabinet.
 

Reply to Rcbo test buttons not working - but works ok when tested in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
638
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
963

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top