c3 for the mismatch of protective device brands
c3 for no ferrules on fine stranded SY in bars
c3 for excess copper showing in that mcb
c3 for the use of SY where greases and heat are present if not deteriorated (also whats been done with the braid)

just my opinion anyway
 
Last edited by a moderator:
c3 for the mismatch of protective device brands
c3 for no ferrules on fine stranded SY
c3 for excess copper showing in that mcb
c3 for the use of SY where greases and heat are present if not deteriorated (also whats been done with the braid)

just my opinion anyway
No code for the mixture of manufacturers’ equipment, as that requirement doesn’t come into force until January the 1st.
No code for lack of ferrules on fine stranded cables, as there is no requirement for ferrules in BS7671.
No code for using SY cable, as there is no prohibition against using SY cable in BS7671.

I am concerned that a ‘C’ type MCB has been installed.
 
sorry spin:
There is a requirement to suitably treat fine stranded conductors in screw down terminals.
SY cable isn't heat or grease retardant so may not be suitable in a kitchen environment.
& we can work to the 18th now.
526.9.1 Connection of multiwire, finewire and very finewire conductors
In order to avoid inappropriate separation or spreading of individual wires of multiwire, fine wire or very fine wire conductors, suitable terminals shall be used or the conductor ends shall be suitably treated.
It does not state “ferrules’.
A long standing practice for protecting such wires is to twist the exposed strands together and then fold them over.

Whilst we are allowed to design, install and initially verify installations to the 18th edition, inspection and testing of existing installations should be conducted to the current edition.
 
Last edited by a moderator:
526.9.1 Connection of multiwire, finewire and very finewireconductors
In order to avoid inappropriate separation or spreading of individual wires of multiwire, fine wire or very fine wire conductors, suitable terminals shall be used or the conductor ends shall be suitably treated.
It does not state “ferrules’.
A long standing practice for protecting such wires is to twist the exposed strands together and then fold them over.

long standing practice it may be but in my book those methods do not prevent damage to the cores, either way it is clear in that picture no methods have been employed at all.
 
526.9.1 Connection of multiwire, finewire and very finewire conductors
In order to avoid inappropriate separation or spreading of individual wires of multiwire, fine wire or very fine wire conductors, suitable terminals shall be used or the conductor ends shall be suitably treated.
It does not state “ferrules’.
A long standing practice for protecting such wires is to twist the exposed strands together and then fold them over.

Whilst we are allowed to design, install and initially verify installations to the 18th edition, inspection and testing of existing installations should be conducted to the current edition.

Hmmm, isn't a ferrule a terminal?

And, in BGB: BS7671:2008:Amd 1:
526.9.1 In order to avoid inappropriate separation or spreading of individual wires of multiwire, fine wire or
very fine wire conductors, suitable terminals shall be used or the conductor ends shall be suitably treated.
 
Hmmm, isn't a ferrule a terminal?

And, in BGB: BS7671:2008:Amd 1:
526.9.1 In order to avoid inappropriate separation or spreading of individual wires of multiwire, fine wire or
very fine wire conductors, suitable terminals shall be used or the conductor ends shall be suitably treated.
No a ferrule is used to treat the end of a conductor.
The terminal is the part with the screw.
In the case of MCBs, the terminals are designed so the screw part of the terminal does not make physical contact with the conductor.
The neutral bar however in the top picture has nothing to protect the conductor from the screw.
 
I hadn't noticed the hinges look nackard in the photo too, and also there's a window for the breakers? how well does that fit? that thing is basically f****'d in so many ways:D :p
The reason the hinges are nackard is because there is a water pipe obstructing the opening of the lid and it has been forcibly opened in the passed.
 
Does it require earthing?
It’s not an exposed-conductive part as it’s under the clear sheath.
It’s no use as a CPC.
I doubt it would function as an earthed metallic sheath if the cable were penetrated by a metallic object.
Good point,Swa as a covered sheath,& not always used as cpc,but is earthed
 
No I haven't but I can tell you it's a Hager. I won't be going back as after pointing a few things out to the owner he has appointed another electrician to do the report.
in other words he wants a tick-box satisfactory report for peanuts. yous best off out of there.
 
20p : Containment - when the lid is down is the IP rating achieved? Can the lid be secured so that a tool is needed to open it? If not, then seeing a bit of exposed copper makes me go for my C2 bat. Am I too harsh?
 

Reply to What do you code these? Commercial installation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Understood, ; ) i'll pass it on to a company who do them day in day out i think.
Replies
8
Views
772
It was purely an off the top of my head example, but I'd say - accessible live parts C1 - inaccessible live parts C2 - 10 feet up in a locked room...
Replies
9
Views
566
i notice you mention "fire rated" instead of "metallic" Are we talking about a metal consumer unit? I know its presumed... but just checking
Replies
4
Views
622
I'm currently an Adult L3 Electrician student however there are a lot of industrial and commercial areas that the evening class doesn't cover and...
Replies
0
Views
115
  • Question
It’s a single phase 1500w motor. It has a 6 amps speed controller, distance from controller to fan about 3-4 meters .
Replies
7
Views
680

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks