Memera 2000 fuse box...is it legal now | on ElectriciansForums

Discuss Memera 2000 fuse box...is it legal now in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

as long as it's safe and complies with BS7671, no problem. i assume you mean because it's not metal cased.
 
Someone is telling porkies and only wants your money. Not ideal but not illegal.

Could you possibly post a picture to confirm?
 
it's not up to current regs., but would have been compliant with the regs. at the time it was installed. i would recommend upgrading, but only as a recommend. a bit like an advise on a MOT.it's a matter of choice whether you want to improve the safety of the installation, but not necessary.
there are 3 categories used on a condition report...
C1 is immediate danger. installation unsatisfactory.
C2 is potential danger... unsatisfactory.
C3 is improvement recommended, but satisfactory. i.e safe for continued use.

at worst, the CU might warrant a C3.
 
it's not up to current regs., but would have been compliant with the regs. at the time it was installed. i would recommend upgrading, but only as a recommend. a bit like an advise on a MOT.it's a matter of choice whether you want to improve the safety of the installation, but not necessary.
there are 3 categories used on a condition report...
C1 is immediate danger. installation unsatisfactory.
C2 is potential danger... unsatisfactory.
C3 is improvement recommended, but satisfactory. i.e safe for continued use.

at worst, the CU might warrant a C3.
Thank you that is very helpful. Any ideas on costs?
 
£350 is about right for a dual RCD CU. if you were to go for RCBOs, though, it would be more like £500+. that is assuming that there are no faults on the installation that require rectification.
 
The unit itself is not illegal nor will it fail an inspection on its own.
However the report is considering the whole installation and there are a number of reasons why RCD protection would now be required for some of the circuits which aren't protected in the current installation. These items could be either recommended improvements or potentially dangerous and often the most sensible way to add RCD protection to multiple circuits is to replace the consumer unit.
 
the main disconnecting switch was only on one side.
I presume you don't mean that the internal wiring of the distribution board has been altered so that the isolator does not isolate everything within the DB?

I have seen this done before by a complete idiot, along with all sorts of other nonsense which meant half of the installation ended up needing rewired along with a new DB installed.
 
Was it compliant with the regs applying at the time it was installed?
Is it electrically UNSAFE today?
No problem then
How, if you want to look good to your customer, you might want to recommend an upgrade depending on the situation
 
Does look like there are a number of non-RCD circuits there that would require RCD protection if installed today.
2nd from the right looks like it’s for a shower.
Not sure whether RCBOs are available for that board?
 
Hi - noting your alarm panel in the picture and if this is HMO - your local authority can insist on electrical standards beyond the minimum requirements as part of the licence. If you are in doubt whether an upgrade is required I'd suggest contacting them for advice.
 

Reply to Memera 2000 fuse box...is it legal now in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Question
Depends if you fitted it with an impact driver!
2
Replies
46
Views
5K
I have this Adee Fusadee lightning arrestor in my electrical cupboard, the area I’m in is prone to thunderstorms from spring to autumn so it is...
Replies
0
Views
390
Definitely, although most likely within the accessories. I've often found that once accessories are disconnected the cabling IR is fine. Sometimes...
Replies
19
Views
2K
  • Question
The last couple of de-loops that I have been involved with had the single phase supply replaced with a three phase cutout (as I believe the DNOs...
Replies
5
Views
757

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks